It basically comes down to, ....those that will make an effort to install a ''Working'' TT system or those that have no intention of making any effort and taking that 200 ohm value as a lame excuse to do virtually nothing, because they are in there mind, complying. Of course stability would then indeed have to be overrated wouldn't it, regardless of what any of the multitude of papers written on the subject have to say!!
 
It basically comes down to, ....those that will make an effort to install a ''Working'' TT system or those that have no intention of making any effort and taking that 200 ohm value as a lame excuse to do virtually nothing, because they are in there mind, complying. Of course stability would then indeed have to be overrated wouldn't it, regardless of what any of the multitude of papers written on the subject have to say!!

In the highly unlikely event that I ever again have to install a TT to either a commercial or large residential then yes...I would be making an effort to get a TN value.I say highly unlikely because these days TNCS is almost always available in my area. I still do a lot of TT's,but small scale. The most recent being a small unit supplying a few sockets for small fairground/entertainment use on a playing field,and temporary civil engineering supplies on a sea front site.For those I believe the standard UK sub 200 ohm and RCD arrangement is perfectly adequate,and if it was 150 ohms at the time of installation and when I came back for a 3 month re-test it had risen to 160 ohms it wouldnt worry me in the least.
That said as Skelton stated in a previous post....I regularly go back to TT's I have installed over the years and cant ever remember initial readings varying to any great degree.
 
In the highly unlikely event that I ever again have to install a TT to either a commercial or large residential then yes...I would be making an effort to get a TN value.I say highly unlikely because these days TNCS is almost always available in my area. I still do a lot of TT's,but small scale. The most recent being a small unit supplying a few sockets for small fairground/entertainment use on a playing field,and temporary civil engineering supplies on a sea front site.For those I believe the standard UK sub 200 ohm and RCD arrangement is perfectly adequate,and if it was 150 ohms at the time of installation and when I came back for a 3 month re-test it had risen to 160 ohms it wouldnt worry me in the least.
That said as Skelton stated in a previous post....I regularly go back to TT's I have installed over the years and cant ever remember initial readings varying to any great degree.

You have often stated in your posts, that soil/ground conditions in you're particular area are not good, and that's fair enough as far as i'm concerned. But you can't go making the same assumptions to those posters that work in and around pretty decent areas, where in some cases i personally know near TN values CAN be attained, in some cases pretty easily too.

Personally i would endeavour to initially treat domestics as i would any other type of installation, only backing off, to let's call it the fall back position, when costs are going to be a major factor.
 
  • Like
Reactions: 1 person
We know what it say's, but i'll guarantee you, that virtually every poster that comes on this and other forums, that isn't knowledgeable on TT systems, take that figure in BS 7671 as being the stated maximum and that's what they inevitably will work too!! ...And why i always Poo it off!! lol!!

The whole section on TT earthing needs a thorough sorting out and a bit more guidance wouldn't go amiss either!!

I'm going home (Cyprus) for Xmas this year, and while home, i'll be checking my own TT system. Earlier this year (early summer) it was around 0.93 ohms which has been steadily dropping year on year from around 4'ish ohms.

Here on site, our earth fields were tested middle of last month and recorded 0.17 ohms and 0.21 on the other. The highest value recorded this year was 0.28 and 0.30 respectively, which corresponds to similar test results conducted last year.

It's surprising what can be achieved when you know what you're doing!! lol!!

So that's what you do with your christmas

think I'll eat turkey and have a good time, knickers to the earth rods
 
I think i can find the time to check my TT system Ra value, it's not as if i'm not home just for the one day like!! I'm sure i'm going to find a lot more maintenance issues that need attending too while home. It's always the same when a house is left unattended for long periods of time!! lol!!

Besides, 15 or so minutes to check the safety of an earthing system, isn't the end of the world, well not mine anyway!!
 
I can just imagine you Eng, the missus inside calling you outside "Sweetheart! The turkey needs carving!", "Just a minute dear, it's of upmost importance that I check the condition of my rod first!", "But you did that yesterday dear, and the day before... And the day before that as well?", "Erm, err, no dear, I don't think I did *chuckle chuckle*, what are you like hey dear? *whilst muttering to yourself>>>* crazy old bat, thinks I'm going senile! Tut".

:D
 
  • Like
Reactions: 2 people
15 mins to check your rods? Why?

I suppose you want your ra values.

You would have checked them before? Why don't you just plug in a metre into a socket and loop it, then do your rcd tests?

2 mins max. Which leaves you 13 mins dig your metre out.
 
Engineer54 a "working" earth what the hell is that? Us electricians call it a stable or un stable earth.
 
Engineer54 a "working" earth what the hell is that? Us electricians call it a stable or un stable earth.
He likes a laugh doesn't he
i think that's the difference between an engineer and a sparky though, we live in the real world.
 
E54 is a qualified part p,pat tester .. Ho ho ho
 
Hi,

How do you PAT test an Earth Rod? Is it done in increments from 0 to 200 ohms?

Regards.
 
Just a visual will do
 
You will all regret your comments when he is here later lol

I think Eng will regret telling us all that the first thing he does on Christmas morning, even prior to opening his stocking from Santa, is to test his earth rod!
 
  • Like
Reactions: 4 people
He must have very long legs.
It's what he gets every year, a bundle of 2.4m rods in his stocking.

And instead of a Christmas card, he gets a brand new Cal Cert for his Earth Tester.
 
  • Like
Reactions: 3 people
I'm waiting for the thunder clap when the time zone in China or Cyprus comes round.....

- - - Updated - - -

Popcorn ready, blanket on knees.

ok go.
 
  • Like
Reactions: 1 person
Nah! E54s bark is worse than his bite lol, he is just a big ol' ----- cat lol

He won't be bothered about us p*** taking about his "rod measuring activities" ooer missus lol , whether over Christmas or not.

If you really want to make him bite, try telling him a 200 ohm rod is just as good as a sub 20 or less ohms one lol, better still a ''twig' is just as good as well
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Max Ze for TT system
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
137

Advert

Thread statistics

Created
MBEINST,
Last reply from
Guest 004,
Replies
137
Views
59,730

Advert