What the foot note on the model form says is...
"Where the maximum permitted earth fault loop impedance value stated in column 8 is taken from a source other than the tabulated values given in chapter 41 of this standard, state the source of the data in the appropriate cell for the circuit in the 'Remarks' column (column 25) of the schedule"
So it doesn't state you must record the 100% value, only that if it isn't from BS 7671 that you state where you got it from.
"Where the maximum permitted earth fault loop impedance value stated in column 8 is taken from a source other than the tabulated values given in chapter 41 of this standard, state the source of the data in the appropriate cell for the circuit in the 'Remarks' column (column 25) of the schedule"
So it doesn't state you must record the 100% value, only that if it isn't from BS 7671 that you state where you got it from.