Just for my sanity... Are you saying that if the Max Zs value for the respective circuit exceeds that of 80% we should instead input 1667 instead to allow for the Max value for a 0.03mA RCD? In the Max Zs field?

On an EICR I would yes.

I would not on an EIC unless it was designed to be.
 
Hummm. Horses and courses n all that. I'd complete the field as required and complete the 30mA section so the certificate detailed the correct OCPD and associated Max Zs and/or RCD type.

Can anyone shed any light on this? Have they had this discussion with their area engineer?
I’m not sure why you would need the discussion with your area engineer? What value would you record on the schedule if it was TT....The max Zs value of the OCPD or the max Zs permitted for the RCD that’s providing the earth fault protection? It’s clear to me what you should be doing.
 
Hummm. Horses and courses n all that. I'd complete the field as required and complete the 30mA section so the certificate detailed the correct OCPD and associated Max Zs and/or RCD type.

Can anyone shed any light on this? Have they had this discussion with their area engineer?

I do not need to speak to my NICEIC Engineer. I understand what is required.

How else would you meet disconnection times if the Zs is too high?
 
Is there an excerpt from BS7671 that details this (Use of max RCD values) over the Max Zs of the OCPD when considering Zs values that exceed the 80% factor?
 
Is there an excerpt from BS7671 that details this (Use of max RCD values) over the Max Zs of the OCPD when considering Zs values that exceed the 80% factor?

To be honest the use of an RCD to cover fault protection on a TN system is not ‘textbook’. But sometimes you need to think outside the box. There are otherways to combat this issue, which is only an issue due yo poor design but it is completly unrealistic to rewire a circuit due to high measured Zs when an RCD will provide protection and still meet 7671.
 
To be honest the use of an RCD to cover fault protection on a TN system is not ‘textbook’. But sometimes you need to think outside the box. There are otherways to combat this issue, which is only an issue due yo poor design but it is completly unrealistic to rewire a circuit due to high measured Zs when an RCD will provide protection and still meet 7671.

Absolutely! Couldnt agree more. But is there an excerpt for stating one value over the other? Or is this just an understanding you have with your engineer. I'll definitely raise this with mine tomorrow if thats what you guys/girls are doing and its deemed acceptable.
 
Absolutely! Couldnt agree more. But is there an excerpt for stating one value over the other? Or is this just an understanding you have with your engineer. I'll definitely raise this with mine tomorrow if thats what you guys/girls are doing and its deemed acceptable.

I don’t run anything by my engineer.

You used the value of whatever the OCPD is that you are using.
 

Reply to Max Zs on certification in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Following on from another thread on here, can you please help me with a fundamental issue regarding certification bodies. Bear in mind we are new...
Replies
11
Views
2K
Hi all. I am collecting evidence for a report on the current 'strategy' and trust given to the competent person schemes by the Communities and...
Replies
13
Views
2K
D
Hi I was wondering if anyone could fill me in here. I tested an installation for someone which consisted of 2 circuits to a loft conversion I...
Replies
4
Views
943
NJG28
N
Hi guys i know this has been done do death, i have searched but i've not been able to find an answer. I'm having a mental block so just thought...
Replies
5
Views
2K
Hi guys, im new to this forum so go easy please ;) I am 17Th Ed and Part P Accredited. Have been doing electrical work for years ( commercial...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock