Discuss Maximum kW anyone has on single phase? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Max105
I (well, the MCS installer) obtained approval under G59 back in 2015 for 11.5 kW of grid connection on a single phase. 12kW of panels into two 6kW inverters. I'm in a fairly remote area. Not aware of any other solar arrays feeding into my local pole mounted transformer.
I'd now like to add more, perhaps another 4-5 kW to take it to maybe 17kW. I will be adding a battery at some stage but not right now, so for now I'd like to add to the existing grid-tied system.
I am interested to know what is the maximum power anyone has managed to get approval for on a single phase here in the UK? Is there an official limit or is it simply case by case basis? What is the theoretical maximum?
My incoming supply is 100A (judging by the size of the fuse).
Please - No advice on adding/extending FIT arrays etc. - Just need the technical limit on known actual real-life examples or specs for DNO limits for grid injection for single phase.
Thanks for looking.
No answers so I guess nobody has achieved DNO approval for more than 11.5 kW export on a single phase?
Anyone here from any DNO (or anyone at all) that would know definitively what the maximum allowed would be?
Max
Max
The max is network dependent. It will be down to the sizing of the cables on the DNO side, whether you have a other generation on their supply side, local loads in the area etc.
I've never heard of anything over 10kW on a single phase supply.
There are export limitation options available now on many new inverters, they work with a CT around the incomer. This is quite common now on larger commercial systems as there's a blanket export limit on some DNO areas.
As above, the DNO have many factors to consider when allowing power export, not just the current carrying capacity of their network but also if it would risk pushing the supply voltage above the limits of the ESQCR (i.e. opposite of voltage drop on load).
Reply to Maximum kW anyone has on single phase? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Hi I have three phase installed recently to increase generation. DNO approved the extra 2 solar arrays so we have 3.68KW FIT on one phase and 8KW...
I currently have solar array and was going to purchase Shelly EM to monitor Grid in/out and solar production. So far so good. But I also plan in...
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
6K
Hi, Similar'ish question to my other thread but little more info now so a different approach but sorry if duplication. UK, single phase. Just had...
Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...