Discuss Mcb rating shower in the Australia area at ElectriciansForums.net
B
bathroomboy
Installing 8.5kw shower which will pull 37 amps, looking at shower cu with rcd, but it comes with 50a mcb will it be ok to overrate or should I change the mcb to 40a.
You would be better of fitting a 32A as mcb should be the same as or lower than the current carrying capacity of the cable as your mcb is meant to protect the cable if I remember correctly thats for 6mm cable or as the post above
Chris
Chris
Hi
Ib should be less than or equal to In, and In should be less than Iz. Not In less than Ib...
Regards
Reply to Mcb rating shower in the Australia area at ElectriciansForums.net
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Hello guys n gals, Did n EICR other week in a flat where the shower circuit was 40A mcb with RCD protection, 6mm cable. Only about 10M run. The...