bathroomboy
Installing 8.5kw shower which will pull 37 amps, looking at shower cu with rcd, but it comes with 50a mcb will it be ok to overrate or should I change the mcb to 40a.
Discuss Mcb rating shower in the Electrical Forum area at ElectriciansForums.net
Installing 8.5kw shower which will pull 37 amps, looking at shower cu with rcd, but it comes with 50a mcb will it be ok to overrate or should I change the mcb to 40a.
You would be better of fitting a 32A as mcb should be the same as or lower than the current carrying capacity of the cable as your mcb is meant to protect the cable if I remember correctly thats for 6mm cable or as the post above
Chris
you sure about that acat nobody mentioned the installation method but method C 10mm is fine on that mcbDecided to have a look if you use the 50A mcb provided it should be on a 16mm cable
Chris