Discuss MCB size and wire size for an electric oven and induction hob in the UK Electrical Forum area at ElectriciansForums.net
Hello
I have two new appliances
Electric oven rated at 3.95 KW
Induction hob rated at 7.2 KW
total of 11.15 KW
Currently it is on its own supply with a 10mm Twin and Earth and the MBC is 32amps
Can you please advise if the following
Cable size is sufficient ( behind plaster )
MCB Amp needed and can I use the new ones now as my cu is old
Thanks in advance
Diversity for a domestic oven/hob is usually taken as 10A + 30% of the remainder.
11150W = 48.5A, so 10A + 30% of 38.5A = 21.5A.
Thank you for your reply, so I don't really want to run a separate circuit to split the oven and hob up.
so with this calculation do you think I am ok ?
Would you upgrade the MCB to 40Amp or 50Amp
I have and older contactum
thanks
thanks
The calculation that Brian did for you took into account both appliances.
I tended to treat a job and oven as two separate appliances, when applying diversity’s, but with only my thumbs to count on, still think that’s ok?
Reply to MCB size and wire size for an electric oven and induction hob in the UK Electrical Forum area at ElectriciansForums.net
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
hi looking to install a new induction hob to current wiring . the wiring i have is thick white probably about 15mm wide and is hard wired into...
Hello, Looking at changing out my gas hob for the PIV851FB1E Bosch Induction Hob. The Induction hob is 7400W and by my calculations this would...
Hi All, I'm looking at installing an induction hob in my kitchen (upgrade from gas) and I gather that it can be added to the cooker circuit if...
