J
Jaxo
I recently bought a megger 1730 and i`m getting some weird earth loop readings using the no trip function. I know they can be a little higher at times when taking a "no trip" reading as my old 1552 was always a little higher too but these seemed well out...
I only got the meter this week (Used from ebay, but in as new condition). I did a few tests around the house and all seemed fine, Then today I had to use it to test a rewire I did in Belfast and thats when I noticed the odd readings..
ZE: 0.28Ω (which I did think was a little high, but within the limit for a PME all the same)
R1+R2 0.17Ω
Earth loop 1.03Ω
This is just one circuit, but they all seemed to give high readings.. I didn`t bother shorting out the RCD`s to take high readings and compare.. It was a friday and I wanted to get home ;)
I had a google in work and some where saying it could be the 500Ma leads and others saying the batteries etc and I did notice the batteries where near dead.. When I got home I charged it and took a few readings around the house and all seemed fine, ZE 0.11Ω , R1+R2 0.41Ω, No trip earth loop 0.61Ω ...
Strange.. anyone else having these problems with the 1700 series Meggers?
The meter is like new, infact there is not a mark on it,.. It didn`t however come with a calibration cert so I`ll need to go in and get checked but just concerned I may have bought a duff one...
When the batteries become low then the readings provided by these meters are not reliable, I would expect this is what happened.
However it is possible that there was a high resistance RCD or MCB in the board that was bumping up your readings.
As you say the no trip test is somewhat variable anyway.
as has been mentioned...
Batterys
Test leads
go for the obvious first...then move on....