This is an extract from an ECA circular, hope it helps:
Periodic Inspections for Older Installations
(a) For 63 Amp and 80 Amp cut-out fuses, 16 mm2 meter tails are correctly sized for both free air
or clipped direct to a surface installation methods and no comments are required. See note (i).
(b) For 100 Amp cut-out fuses and 16 mm2 meter tails installed in free air, the following wording
should be entered onto the PIR "It is recommended that the meter tails in this installation be
replaced with 25 mm2 size if and when the service head or service meter is replaced".
See notes (i) and (ii).
(c) For 100 Amp cut-out fuses and 16 mm2 meter tails installed clipped directly to a surface,
Code 2 and the following wording should be entered onto the PIR "The meter tails in this
installation require either re-installing in free air or replacing with 25 mm2 size tails". See note (ii).
Notes:
(i) For meter tails installed in walls, trunking or similar, further de-rating is required and the
following sizes should be present:
Cut-out size
Installation
method
Minimum size
63 Amp In trunking or conduit
(ref method B)
16 mm2
63 Amp In trunking or conduit buried in an insulating wall
(ref method A)
25 mm2
80 Amp In trunking or conduit
(ref method B)
25 mm2
80 Amp In trunking or conduit buried in an insulating wall
(ref method A)
35 mm2
100 Amp In trunking or conduit
(ref method B)
25 mm2
100 Amp In trunking or conduit buried in an insulating wall
(ref method A)
50 mm2
(ii) The free air rating of 16 mm2 cable is greater than 100 Amps but DNOs specified a size of
25 mm2 for cut-outs of 100 Amp rating.
(iii) Where the size of the cut-out fuse cannot be ascertained, then the inspector has the option
of either assuming 100 Amp size, or contacting the DNO.
(iv) The thermal withstand under short circuit conditions of is not a limiting factor on the size of
cables required.