I have an old panel that produces 8 x 240v outputs to signal lamps, I wish to use these outputs to run a mimic panel a distance away, I need 110v to deal with the volt drop, but dont want 240v at the mimic, thinking of 240v relays in the master panel and running a multicore swa carrying my signals from a 110 control supply, anything on the market that will make this job easier without using radio signals.
 
its not a safety circuit as in control, but the indication has to fail to safe
[h=2][/h]ie power loss what would you see, or cable is cut shorted etc
 
You seemed set on using 110v instead of ultra low 5v or 12v, and using multicore. Signal switching will eliminate voltage drop, and 200m or 300m can easily be achieved using standard control cable
 
That's not a bad idea if I can fire relays at 12v over that distance, and 12v leds would be fine too
The idea is to switch signals which inturn switch relays, and if fail or cables are damage go in fail safe....this is the basic principle of a security alarm, switching micro Amps on a door contact, hence no worries on voltage drop, or heavy cable use
 
so if i have the 240v signals operating relays in the control panel I can then have a nice little 240/12 tx to run 12v through those relay contacts, giving me my 8 12v signals heading down my multicore which in turn can operate 8 12v relay coils in my mimic with which I can produce lots of outcomes, especially if i intoduce a backup supply locally
 
some require two signals to be present before showing indication, there will be two colours interlocked only one and not the other etc, that's simple once I have my relays in the mimic with a signal to each one
 
Well again logic switching before the relay can be used......if this is only for indication purposes then no relays are required, on the mimic panel, just basic 30p logic 4000 series ic`s they can drive leds on there own
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
mimic signal panel?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
34
Unsolved
--

Advert

Thread statistics

Created
Richard3009,
Last reply from
Knobhead,
Replies
34
Views
3,962

Advert

Back
Top