Newbyspark

Another one

Describe 3 types of wiring system that are permitted outside of the prescribed zones, when buried 30mm deep in a wall?
 
Another one

Describe 3 types of wiring system that are permitted outside of the prescribed zones, when buried 30mm deep in a wall?

Think about Part P (50mm from finished surfaces, what do you need?) and also cable protection for this install? Where does that lead you to????
 
522.6.101 (BGB) ? :)

This is interesting as i was not aware you could install cables buried in a wall outside of the zones? Does earthed mechanical protection change this?

Surely it still needs to be within the zones RCD/Earthed mechanical protection or not?
 
I was told today, it is earthed S.W.A, earthed metallic conduit and earthed metallic trunking.
 
I think it was the way i read it to be honest.

Having had a closer look at 522.6.101, it makes sense. :book:
 