N

Newbie90

Hi all,

I have a Fluke digital multimeter and whilst testing live to earth on a controller, it tripped the rcd.

Can anyone explain why?

Is it like the fluke t120 voltage indicators where you have to test between live and neutral for 5 secs beforehand?

Thanks
 
Should be a low current test, if it is and its still tripping try reversing the polarity of the test, ie live down earth and earth down live, some of the new rcds have this problem and reversing the polarity seems to solve it, also make sure there are no loads on the circuit
 
i would hope that you were measuring voltage, not current. it would seem that the meter is drawing sufficient current to trip the RCD.
 
Can't believe a digital multimeter would draw enough current to trip an RCD, my money's on the 'using it as an ammeter' theory. Daz
 
When you say it has to be held on live to neutral for 5 seconds is that for the continuity buzzer to work. I had an alphatec that would trip rcds If you tested on live to earth before live to neutral as charging the internal capacitor that powered the buzzer drew enough current to trip most rcds. Useless it was and had a very short spell in my toolbox.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Multimeter tripping rcd...
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8
Unsolved
--

Advert

Thread statistics

Created
Newbie90,
Last reply from
power ranger,
Replies
8
Views
18,149

Advert

Back
Top