I've recently upgraded some light fittings that are probably 15-20 years old in an industrial unit to LED fittings
  • 150W Low bay LED's internally
  • 80w LED light fittings with separate photo-cells on external lighting column opposite warehouse.
Is there a requirement to issue a MWC
 
i would. with test readings of the circuit/s to ensure compatibility with the new LED fittings and compliance with BS7671.
 
Has the wiring been altered? If not then no (unless the client has requested one), although appropriate inspection and testing must still have been carried out.
 
If you decide not to, though I would be inclined to due to testing, you could add test results to invoice so that it is recorded. MWCs are usually quick to produce and carry the results in appropriate boxes.
 
I don't understand people who tack on test results to an invoice.
 
  • Agree
Reactions: Rpa07 and Risteard
It’s not required by BS7671.
Would probably help to tick some boxes under CDM Regulations.
Could make a mention in the invoice about ‘tests conducted to verify suitability of circuit/installation for replacement of fittings’.
 
Another one with invoice add ons.
 
Another one with invoice add ons.
Not really, unless all your invoices just state the price and don’t detail what it’s for.
My invoices say things like:
2 X Light fittings £490.
Labour 2 hours £100.
Parking £2.30.
Sundries £5.00.
Verification tests £25.
 
I am not seeing any test results as some are stating.
 
  • Agree
Reactions: Risteard

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
MWC - Required or not - LED Light fittings
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
DemoElec,
Last reply from
Deleted member 26818,
Replies
12
Views
1,840

Advert