I installed a Reliance Transfer Switch on my home. 8 of the 10 circuits are working correctly. 2 of the circuits are operating GFCI outlets. After hooking everything up, the GFCI outlets stay tripped. They will not reset. Who do I need to do?
 
Does the problem occur with generator power only, grid power only or both? What voltages are you getting at the circuits feeding the GFCIs (Hot-neutral, Hot-ground, neutral-ground) ? How is the neutral / ground bonding arranged on the generator hookup?
 
Does the problem occur with generator power only, grid power only or both? What voltages are you getting at the circuits feeding the GFCIs (Hot-neutral, Hot-ground, neutral-ground) ? How is the neutral / ground bonding arranged on the generator hookup?
Grid power only. I haven't even hooked up the generator yet.
 
Are the correct voltages present at the GFCIs i.e. 120V hot-neutral, 120V hot-ground, near 0V neutral-ground?
 
If all three voltages are correct and the right way round, it's possible that there is something high-resistance that tests OK with a multimeter but falls out of spec when the GFCI tries to reset. With the power off, I would try continuity tests from the outlet to the transfer switch, to make sure for example that the neutral isn't high-resistance at the transfer switch. Which Reliance model is it?
 