I'll make this as short as possible.

This is what I have:

1) Inverter: Aukey 1000 W
2) Solar Controller: 40A
3) Battery: Solar battery 100 Ah C100
4) Solar Panels: One 100W PET Panel

I want to follow this:

50595


My Question:

What Amp fuse do I need to/from everywhere? (Yes, I'm a noob, this is my first project)

The fuse go to a fuse holder then connection right?

Can I use a circuit breaker instead of fuse?

Update: Sorry forgot to add 12V
 
Last edited:
12 AWG is usually rated at 20A.
Though a 100W panel at 12V will produce just over 8A.
So anywhere between 8.5A and 20A should be fine.

4AWG is usually rated at 70A.
However the Solar controller is rated at 40A.
So anywhere between 40A and 70A should be fine.

Make sure you also use 4AWG for the negative side between the battery and the inverter.
 
12 AWG is usually rated at 20A.
Though a 100W panel at 12V will produce just over 8A.
So anywhere between 8.5A and 20A should be fine.

4AWG is usually rated at 70A.
However the Solar controller is rated at 40A.
So anywhere between 40A and 70A should be fine.

Make sure you also use 4AWG for the negative side between the battery and the inverter.
Thank you so much!
 
spin is correct in saying the controller is 40A. however, with a fully charged battery and the inverter supplying it's full load capacity of 1000watts, that's 83 A @ 12V,
 
83.3333 to be exact. maybe a little over to allow for losses in inverter.
 

Reply to Need help with fuse in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Can I add solar panels to an existing system without jeopardising my feed in tariff? I have a 3.8kw system but was thinking of adding a few more...
Replies
10
Views
3K
Hi, I plan to add solar to my home and have a question about how many amps I can backfeed into my AC service panel using Net Metering. I know NEC...
Replies
1
Views
796
Hello, I am a homeowner and have a solar project coming up. I intend to install a 9kw solar system but I am not sure if I have to upgrade my main...
Replies
2
Views
927
I am a retired Electrician and started looking at Solar Power, (Black Magic to me), after much reading of "How To", I decided to build myself a...
Replies
10
Views
1K
I (well, the MCS installer) obtained approval under G59 back in 2015 for 11.5 kW of grid connection on a single phase. 12kW of panels into two 6kW...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock