When is an earth neutral link required in an main switchboard? Is it particular to the earthing system?

Is it common to earth the source neutral at the first point in the LV system where the neutral is terminated - the main LV switchboard.

If the Neutral terminal of the transformer is grounded near the transformer and if it is interconnected with the other earth rods/bars? Is still neural - earth link to be provided at the Main switchboard?
 
Is it common to earth the source neutral at the first point in the LV system where the neutral is terminated - the main LV switchboard.

If the Neutral terminal of the transformer is grounded near the transformer and if it is interconnected with the other earth rods/bars? Is still neural - earth link to be provided at the Main switchboard?

1 - Yes it is common, most have it, but some may not.
2 - Yes it is still neutral. it is simply using earth as a means to get home.
 
If REF (Restricted Earth Fault) monitoring is being used the N→E link will be in the main switchboard. Otherwise the link can be at the transformer or the switchboard, it’s up to the designer.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dammam, Saudi Arabia
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Neutral - Earth link in Main Switchboard
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
charzree,
Last reply from
Carl S,
Replies
2
Views
7,933

Advert

Back
Top