head is battered its been a bad day and cant think straight.
Replaced a 3kW water heater element and everything went well. Circuit tested out fine so turned everything back on but when the element is pulling im getting L-N 238 L-N 234 N-E 4V!!! This was tested at element but is the same at the supply side of the 13A DP FCU but at the board (3phase) N-E is nothing (well mV anyway) When element or FCU is off everything is normal
I have checked all relative connections and even checked another heater on site and it is the same.
Is this just the way elements are?
Why would the supply side of FCU have 4V but the board not?
cheers all have a good weekend and some lovely cold beers
you could use the 4V to charge your mobile. other than that, don't fret. could be induced voltage. try measuring with an analogue meter.
Welcome to the world of volt drop. You get VD* in the neutral as well as the line. Hence the 4V between N and E at the load.
(Deleted a load of waffle)
*(Sounds like a trip to the clap clinic is due).
But the following figures and the drawing are right
The 4v is probably just voltdrop on the neutral as Tony mentioned.It might be worth doing a visual earthing check and an earth impedance test, if the earthing is tn c s it's a little higher than I'd expect to see.
unless your a BG engineer!! 4v is deadly and they need to upgrade all your earth and bonds and remove your split load box and install a dual rcd.... not to mention replace your boiler and pipework!!
all because his volt stick LIT up...!!
Its not Induced voltage. Its VD.
Doesn't matter what earthing system it is, If you'v got VD, you'v got VD mate!!!
It'l be same on any system.
You get VD under load conditions. Its normal and nothing to worry about. It shouldn't be more than 5% for an immersion heater.
i might be having a blonde moment here. understand there is probably a bit of a VD under load, say there's a VD of 4V L/N. why is that not 4V L/E as both N and E are assumed to be 0V. so therefore 0V N/E?
There’s volt drop along the neutral. At the source (the CU) N and E should be more or less equal. At the point of load there will be a slight rise between N and E. 4V will give a total of 8V for the entire L/N loop. Which equals 3.47% volt drop, perfectly reasonable.
If the current is high enough that the l and n wires become part of the load and an equal voltage would be dropped across each. At the immersion heater you could get a 4 volt reading between n and e but the closer you get to the n-e bonding point on tncs the n-e voltage should get less. I actually misread part of the OP where he says he measured 4v at the FCU. I thought he was talking about the CU. All the terms like FCU and CU are not used here so occasionally I translate incorrectly so the blonde moment is at his end not yours :(
thanks for that, tony. i'm just trying to get my head round it. i see why, but not how, if yo know what i mean. :28:
guys,
I think what you mean is that
L-N voltage is 234V
L-E Voltage is 238V and
N-E Voltage is 4V
Quite normal.
telectrix:-
Volt drop in the neutral wire when under load, therefore Neutral voltage at load end relative to MET = 4V
No voltdrop in earth wire as no current flow in it, Therefore CPC voltage at load relative to MET = 0V,
therefore N-E = 4V
i can see the logic in that. just VD in the neutral is hard to grasp. a few more beers and all will become clear.
i'm getting there, tony. can see it clearly from your diagram. many thanks.
now that would put the cat amongst the pigeons. TC, don't you dare! LOL.
I have been having a quite night but after trying to get my mind round this I think it's time to reach for a bottle.
The way I understood this phenomenon was simple physics:
A is a measure of the number of electrons passing a point per second.
V is the potential difference so the force pushing the electrons along.
In plumbing speak the A is the volume of water and V is the pressure or head.
In a circuit the electrons will take the easiest route to ground. For example if you short E and N a RCD will trip. Back to plumbing speak equivalent of puncturing the pipe.
The electrons are all being squeezed through a small section of copper and therefore encounter resistance - V=I R. The back up due to resistance is the V measured between E and N. It is 0 at the consumer unit as this is near where E and N are merged tnc (not tt) so there is no relief of V by shorting N and E.
This leaves vd. Is this not caused by the resistance in the cable v=ir. E.g. If 10a of current flows through cable with 1 ohm of resistance the vd is 10v?
I am now going to pour a stiff one. Would be grateful for some clarity on this.
In a circuit the electrons will take the easiest route to ground. The electrons are all being squeezed through a small section of copper and therefore encounter resistance - V=I R. The back up due to resistance is the V measured between E and N. It is 0 at the consumer unit as this is near where E and N are merged tnc (not tt) so there is no relief of V by shorting N and E.
Physics????
A lot of mumbo Jumbo if you ask me!!!!!!
Iv'e never seen any electrons or even been shown any at the college.
Its not electrons, its positrons that flow when a current flows.
Thats marvellous, but I still don't quite understand!!!!
Think of it as 3 resistances in series, 1 for the Line conductor, 2 for the load and 3 for the Neutral.
As you well know (!) voltage is dropped across a resistor.
In this case the load resistance is much greater than the conductor resistances, so the vast majority of the voltage is dropped across the load and small amount on the conductors...
Clearer??? :)
no that the waters are well and truly muddied, i realise why i neve rdrink water ( apart from what fish do in water)
Physics????
Maybe when Moses was a lad but when I went to school an Amp was a coulomb of electrons passing a given point in a second. Tbh though I haven't seen an electron or proton either!
I thought lineProducts comparison with pipework and water was a good descriptive post
Voltage drop causes electricians to have nasty traits
It also tends to diminish with understanding
If you think of the N cable as having some resistance (as will the L conductor).
it will be possible to pull the N conductor at the end nearest the load towards the load (supply) slightly (raising it by 4V in this case) as it (the N conductor) has a slight VD along it's length, which is proportional to the current it is passing.
the E conductor meanwhile has no load on it, as it is not passing any current, hence the slight discrepancy.
Tony may be able to post the vector/phasor drawings better than I can.
You are a magician!!!!
The OP does not tell us the 242V figure.
Where did you get it from????????
You sure that's r8????
If you have 4V drop in the neutral then it stands to reason there will be 4V drop in the line. So 234V across the load plus 4VD on each line equals 242V at the source.
Based on a good N/E connection.
I’ve realised I made a cock up in my first post so I’ve highlighted it in red. Sorry for any confusion, but all the figures and the drawing are correct.
Physics????
And there was I, believing my old lecturer when he taught us it was all about electron-hole-pair movement....
guys
thanks for all the responses and a lot of it makes sense. I can see the VD situation been the most probable cause now but if this is the case I dont recall seeing this on a lighting circuit at the same site when I replaced some fittings few month ago?
Of course I shall check when im there next week again
I love this weather, im off to pick up some beers :)
Surely if you pull the N conductor it will stretch and get thinner and increase its resistance and all your maths will be wrong and to be done again.
What are you saying now, we have to fit the non-existent electrons in to Holes now?
This is just silly and a farce!!!!
How can you put something into a hole when you can't see it in the first place.:flowers:
And the dish ran away with the spoon!
Reply to neutral-earth voltage in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
A silly fault in a circuit only 4m long is currently eluding me! This is ECIR remedials of a landlords supply in a block of flats. Circuit 2 =...
Hi Guys, Had a call out today about an odd issue with a newish Creda DT storage heater. Basically.. Storage heaters were installed in one flat...
A client has a Kenwood CK405 dual fuel range cooker, for which the smaller of the 2 ovens doesn't work. The elements tested out fine, but live...