HI all,

customers are building a small house and im coming off thier PME supply to the new build, 25mm 3 core SWA, small two bed house about 40mtrs away

builders have put another MEB box next to the existing one and im fitting a metal clad switch in with 100amp 100ma time delayd RCD to RCBO board in new build.

can i export the earth or should i TT the new house, trouble is ive got metal boards both ends so if i TT it ill have to take the SWA out of the new build board and terminate it into a plastic enclosure first to isolate the PME earth then off new build board to spike, that seem right people?

Cheers
Grand
 
As you have 3-core 25mm the CPC core (in addition to the armour) is plenty good enough for earth bonding to any extraneous parts in the new property so just use that.
[automerge]1591944284[/automerge]
You should also be providing short circuit protection for that cable, presumably you are feeding it with a 80A or similar fused-switch from splitting their meter tails?
 
Hi - as per Buzz, I like a new supply for a new dwelling. If they’re getting planning for a separate residence, just saying. Perhaps calc the final loop impedance as it may be a bit high after adding 50m of cable to it.

Personally, I like TT for outbuildings probably because it’s easy to get a good result in my area and I’m lazy striving for excellence :) .
 
Last edited:
If this is a temporary supply then fine I would advise the builders not to do this as a permanent supply.
A number of years ago I got involved in a job where a farmer built a granny house on his land and supplied it from the farm, several years later granny died and the farmer decided to sell the house, sale was agreed but then the buyers solicitor found that the house was fed from the farm, cost the farmer a fortune getting a DNO supply, in a short time frame.
 
Perhaps calc the final loop impedance as it may be a bit high after adding 50m of cable to it.

Personally, I like TT for outbuildings probably because it’s easy to get a good result in my area and I’m lazy striving for excellence :) .
If it is an all-RCBO board and/or has a 100mA incomer then you can use either a rod for TT or the CPC extended from the original PME supply, as either is low enough Zs to meet the disconnection requirements.

Lazy option there is to use the supply earth!
 
By doing that lose a neutral then you are buggered it would be better to TT it.
I guess it comes down to how likely is a PME fault and you being in contact with true Earth, versus how reliable your TT rod is.

In most cases having the supply earth will lead to disconnection on the over-current trip so the RCD is "additional protection", but on a rod the RCD be comes primary protection. Of course if you have both a incomer delay RCD and RCBO then you don't have that single point of failure and you need not worry about having your extraneous parts touched during a fault...
 
builders have put another MEB box next to the existing one and im fitting a metal clad switch in with 100amp 100ma time delayd RCD to RCBO board in new build.

You need a fuse in there not an RCD, and yes use the DNO provided earth.
[automerge]1591997842[/automerge]
By doing that lose a neutral then you are buggered it would be better to TT it.

It will be exactly the same as every building that is fed from a PME supply, so by your logic here every installation with a PME supply should be converted to TT.

It is better, in my opinion, to use the PME earth and install supplementary earth rods connected to the MET.
 
Last edited:

Reply to New Build house off existing supply, export PME or TT in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning all, long time reader first time post so looking for some help I’m qualified as an electrician but haven’t worked as a sparky for...
Replies
5
Views
2K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
692
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
855
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
834
Metal shed In Garden with no extraneous conductive parts House electrics PME supply Garo make a 40a PME fault detection unit for EVs and I was...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock