I seem to recall that temporarily rodding it (albeit with a higher Ze) although on the surface that seems counter intuitive, was to provide a stable "known" if higher Ze, the reasoning behind this was that the TNS earth has already deteriorated and could totally fail at any given point in time leaving the install with no earthing whatsoever, in this sense the TT was the better option until the DNO come out and sort it.
uless, of course, you bang the rod through the DNOs incomer.I seem to recall that temporarily rodding it (albeit with a higher Ze) although on the surface that seems counter intuitive, was to provide a stable "known" if higher Ze, the reasoning behind this was that the TNS earth has already deteriorated and could totally fail at any given point in time leaving the install with no earthing whatsoever, in this sense the TT was the better option until the DNO come out and sort it.
my dad did that XD stupid labourer/builder has ripped up many service cables with jcb'suless, of course, you bang the rod through the DNOs incomer.
I seem to recall that temporarily rodding it (albeit with a higher Ze) although on the surface that seems counter intuitive, was to provide a stable "known" if higher Ze, the reasoning behind this was that the TNS earth has already deteriorated and could totally fail at any given point in time leaving the install with no earthing whatsoever, in this sense the TT was the better option until the DNO come out and sort it.