Apply diversity across each isolator block and you get approx: 83A rings 32A dryers 100A heaters 5A lights 10A controls using likely current demand rather than CB sizes total 230A OK for main switch and 3p isolator.
If it is an installation in use and the fuse has not blown then max demand is <250A (rating of main switch).
If you are designing it I would do diversity normally for socket rings 32A each (100% biggest+70%), dryers would be about 10A each (100% first 75% rest). Heaters about 13A each (100%+75%), lighting assume about 5A total draw (not much on it, maybe 10 100W items), controls take very little but assume 10A.
Rings are way over cut as they will not take this much (as it would overload the isolator rating) so could drop that a bit.