Discuss Nightmare of a day. RCD tripiing under any load in the UK Electrical Forum area at ElectriciansForums.net

What's confusing me is why when I plug anything into kitchen socket covered by RCD A is it tripping RCD B? Surely this means it can't be a N to E fault as it would trip RCD B if this was the case

If you have an NE fault on a circuit on one RCD then loading a circuit on the other RCD can cause the first RCD to trip.
Did a diagram for you:
RCD Trip due to other side loading.jpg
 
Every time we get a thread about RCD's tripping after a CU change, the common consensus is either a N-E fault or a shared/borrowed neutral. And every single time the OP has failed to test the installation prior to replacing the old rewirable CU with one containing at least two RCD's.

How many more times do these guy's NEED to be told to test these installations before they start changing them out for god's sake??

What's more, why is this fault causing such a problem to find and rectify. I would have thought that in around an hour, an experienced electrician would have sorted this problem out, ...or at the very least well on his way to finishing off any remedial work...
 
Eng54 do you honestly think in the real world customers would give the go ahead to carry out testing before changing a board? This would mean an additional cost on top of a board change The customer would simply get someone else to do the job!
 
A test for borrowed neutrals plus an IR plus an EFLI wouldn't take very long at all would it?
You've already done enough there to identify any major problems and you're doing the rest of the tests anyway on completion of the change so what's the problem?
 

Reply to Nightmare of a day. RCD tripiing under any load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
377
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
614
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock