wallyanker

Looking for advice please in domestic wiring in an outbuilding.....

An outbuilding connected to the back of a friends house has been converted into a little aviary and has one double socket already in there (spurred from the house RFC, CU has RCD). He would like 2 double sockets and a flourescent light fitting so has asked me to do it. Does this sound the right way to do it?

1. Change existing double socket to 13a FCU and then run 2 double sockets from this.
2. Take another feed from supply side of 13a FCU to 3a switched FCU and then to light fitting, using the switched FCU as the light switch?

Sorry if this seems basic but I dont normally work on domestic.

Thanks for you help
Pete
 
sounds a good plan. only other option , IMO, is if the feed is 2.5mm and you want a little extra power on the sockets, you could fit an enclosure containing a 20A MCB in place of the 13A FCU.
 
Thank you for all replies,

Just re-read my first post and think I got part 2 wrong, the 3a FCU must be fed from the load side of 13a FCU.

Cheers
 
no reason not to feed 3A FCU from the "live " side of the 13A FCU.
 

Reply to Outbuilding wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
785
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
313
Hello. I live in a new build house with a separate garage. The garage is connected to RCD in the house to a 16A circuit breaker. The cable from...
Replies
1
Views
240
Hi, I replaced an outdoor electrical socket recently with a 2 gang, BG socket which has LED lights to show when it is switched on. Since then I...
Replies
19
Views
669
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
763

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock