I'd still of IR tested the install....would take 5 minutes to do a global. As it is you've made an assumption that may be correct but it's still an assumption.
How do you mean 5 minutes to do a global? Usually takes about 20 mins for the occupier to run round and unplug everything. Then you have to spend another 10+ mins working out whats still connected......problems pretty obvious here why complicate it??
 
How do you mean 5 minutes to do a global? Usually takes about 20 mins for the occupier to run round and unplug everything. Then you have to spend another 10+ mins working out whats still connected......problems pretty obvious here why complicate it??
Nah leave it all plugged in, IR to earth job done. Does not more harm than a PAT, if you get problems then unplug.
 
I didn't explicitly say I didn't test the install. I did IR test it and returned fine. Also clamp tested to see but that returned nothing interesting
Nice one, don't make a drama out of it. Problems obvious, no need to conduct an inquest, times money! Tricky concept for some folks.....
 
Nah leave it all plugged in, IR to earth job done. Does not more harm than a PAT, if you get problems then unplug.

Yet another who deviates from the ABC of testing to improve and speed up fault finding in Domestic installs :thumbsup:
After all,it's the fault that needs to be located and that can be installation or user cause,two birds with one stone and all that
 
Do you know the trip current for the main RCD (Ramp test)? And the current board leakage, I have had a couple of houses right on the limit for the RCD, then adding something with acceptable leakage pushes it over the limit.
 
How do you mean 5 minutes to do a global? Usually takes about 20 mins for the occupier to run round and unplug everything. Then you have to spend another 10+ mins working out whats still connected......problems pretty obvious here why complicate it??

Nah leave it all plugged in, IR to earth job done. Does not more harm than a PAT, if you get problems then unplug.

Nice one, don't make a drama out of it. Problems obvious, no need to conduct an inquest, times money! Tricky concept for some folks.....

5 minutes! As above,you are looking for a fault not doing initial verification,so leave everything plugged in and you are more likely to locate the problem.
Over the years I've been to loads of jobs where a previous sparks has disconnected an 'obvious problem' only for the tripping to recur. 5 minutes testing found an issue on a completely unrelated circuit.
Your cavalier approach is a recipe for comeback.
 
5 minutes! As above,you are looking for a fault not doing initial verification,so leave everything plugged in and you are more likely to locate the problem.
Over the years I've been to loads of jobs where a previous sparks has disconnected an 'obvious problem' only for the tripping to recur. 5 minutes testing found an issue on a completely unrelated circuit.
Your cavalier approach is a recipe for comeback.
That's me, specialised subject the bl**ding obvious, as Basil would say.
 