A question reguarding P.E.F.C and P.S.C.C using a megger 1553

Now i know this is a live test so lets say ive safely isolated ive got my megger im using the 2 wire lead option green and red.

So the board has RCD protection so i set my megger to the NO TRIP PFC ? CORRECT ?

Then test between LINE + EARTH for the P.E.F.C
Then test between LINE + NEUTRAL for the P.S.C.C

Then record the highest of the two results which = the PFC worst case scenario ? correct this is on a TNCS system by the way.

help would be appreciated many thanks volt
 
Hi all

A question reguarding P.E.F.C and P.S.C.C using a megger 1553

Now i know this is a live test so lets say ive safely isolated ive got my megger im using the 2 wire lead option green and red.

So the board has RCD protection so i set my megger to the NO TRIP PFC ? CORRECT ?

Then test between LINE + EARTH for the P.E.F.C
Then test between LINE + NEUTRAL for the P.S.C.C

Then record the highest of the two results which = the PFC worst case scenario ? correct this is on a TNCS system by the way.

help would be appreciated many thanks volt

Sounds spot on but if you can test on the supply side of the RCD without using 'no trip' (assuming it's within the DB) then your PFC reading will be more accurate.

The black lead on the 1553 will stay connected to the neutral bar throughout the 2 tests.

Your PEFC and PSSC should be almost identical on a TN-C-S system.
 
If it is on a TNC-S chances are the results would be the same.

As for the Meggar, I'm not a meggar man but I would have thought it would be the NO TRIP setting to be honest.
 
Sounds spot on but if you can test on the supply side of the RCD without using 'no trip' (assuming it's within the DB) then your PFC reading will be more accurate.

The black lead on the 1553 will stay connected to the neutral bar throughout the 2 tests.

Your PEFC and PSSC should be almost identical on a TN-C-S system.

Im a bit confussed now :) ahh forgive me i just noticed on the megger the top hole has the NO TRIP LOOP so this would be the neutral which would be connected thoughout the test ? correct ?

So the test would be a 3 lead test in reality then ? not a 2 as i thought ? is this correct ? many thanks volt
 
Im a bit confussed now :) ahh forgive me i just noticed on the megger the top hole has the NO TRIP LOOP so this would be the neutral which would be connected thoughout the test ? correct ?

So the test would be a 3 lead test in reality then ? not a 2 as i thought ? is this correct ? many thanks volt

I wasn't too clear there, if you can perform the test without using 'no trip' then it's a 2-lead test.

Using 'no trip' it's a 3-lead test.
 
I wasn't too clear there, if you can perform the test without using 'no trip' then it's a 2-lead test.

Using 'no trip' it's a 3-lead test.

Not being a meggar man in the 2 test lead for no trip. Do you have to link the blue/green leads together of just use the red/green leads.
 
I tend to use the Hi setting on the megger (- 4th along on the green area of the dial, if you know what I mean.) 2 lead test for PFC to earth and neutral
 
Don't need to link leads on the megger just have red & green plugged in.


Sent from my iPhone using Tapatalk.
 
I tend to use the Hi setting on the megger (- 4th along on the green area of the dial, if you know what I mean.) 2 lead test for PFC to earth and neutral

yeah i can what you mean on the megger says HI PFC LOOP so this way i could just use RED and GREEN leads ?

So the test would be LIVE TO EARTH ?
LIVE TO NEUTRAL ?
 
yeah i can what you mean on the megger says HI PFC LOOP so this way i could just use RED and GREEN leads ?

So the test would be LIVE TO EARTH ?
LIVE TO NEUTRAL ?

Yes, no need for the 3rd lead on the full test.
 
yeah i can what you mean on the megger says HI PFC LOOP so this way i could just use RED and GREEN leads ?

So the test would be LIVE TO EARTH ?
LIVE TO NEUTRAL ?
that's how it is on the 1552. don't use no trip.
 
Reading through the megger leaflet quick start guide reguarding this PFC TEST

non tripping loop test [NO TRIP]

Select when testing ciruits with RCD protection fitted it says

High current loop test [HI]

for use on circuits with no RCD protection fitted

No trip PFC measurement [NO TRIP PFC]
phase to earth PFC
 
yes, but you only use no trip when measuring after the RCD, not before it
 
yes, but you only use no trip when measuring after the RCD, not before it

Thanks i get it now :)

So the test i would use on my TNCS system and the consumer unit being a MK dual RCD board would be

To set the megger onto the HI loop setting into the green area
then test form LIVE TO EARTH then LIVE TO NEUTRAL and record the highest reading as my PFC ?
 
spot on. remember this test is done with the main switch OFF, and all earths connected.
 
Last edited:
Thanks i get it now :)

So the test i would use on my TNCS system and the consumer unit being a MK dual RCD board would be

To set the megger onto the HI loop setting into the green area
then test form LIVE TO EARTH then LIVE TO NEUTRAL and record the highest reading as my PFC ?
Correct (as long as it is before the rcd) you can do either the 2 lead or 3 lead test before an rcd , but it has to be the 3 lead , no trip option after an rcd.
 
spot on. remember this test is done with the main switch OFF, and all earths connected.

Yeah thanks for that much aprreciated guys got their in the end :) but its so important to make sure its right you have no other option than to be ---- about it [ as one of a better phrases ] :D

I mean obviously im new to this but once i get my inspection out the way i want to take the level 2 testing and inspection to boost my confidence then maybe onto the level 3.

Thanks once again guys for all the replies much appreciated and very helpfull.
 
Yeah thanks for that much aprreciated guys got their in the end :) but its so important to make sure its right you have no other option than to be ---- about it [ as one of a better phrases ] :D

I mean obviously im new to this but once i get my inspection out the way i want to take the level 2 testing and inspection to boost my confidence then maybe onto the level 3.

Thanks once again guys for all the replies much appreciated and very helpfull.

Perfect attitude, pity the perpetrators of much of the certification that I come across didn't have the same pride!
 
Im a bit confussed now :) ahh forgive me i just noticed on the megger the top hole has the NO TRIP LOOP so this would be the neutral which would be connected thoughout the test ? correct ?

So the test would be a 3 lead test in reality then ? not a 2 as i thought ? is this correct ? many thanks volt

Hello voltage

A PFC measurement conducted at the origin of the installation or PSC measurement on the MFT1500 Series requires 2 testleads only (red & green) with the tester switched to the Hi PFC settting (the last settting in the Green loop section on the tester). The connection to the circuit would be at the input terminals of the main breaker/ RCD in the case of PSC measurements or for a PFC measurement the connections would be the incoming phase terminal and the main earth terminal.
The no trip section requires individual connections to phase, earth and neutral for measurements.

Regards

Megger TSG
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
P.F.C using a megger 1553 advice plz
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
voltage,
Last reply from
Megger TSG,
Replies
20
Views
5,736

Advert

Back
Top