Discuss P.F.C using a megger 1553 advice plz in the Industrial Electricians' Talk area at ElectriciansForums.net
V
voltage
Hi all
A question reguarding P.E.F.C and P.S.C.C using a megger 1553
Now i know this is a live test so lets say ive safely isolated ive got my megger im using the 2 wire lead option green and red.
So the board has RCD protection so i set my megger to the NO TRIP PFC ? CORRECT ?
Then test between LINE + EARTH for the P.E.F.C
Then test between LINE + NEUTRAL for the P.S.C.C
Then record the highest of the two results which = the PFC worst case scenario ? correct this is on a TNCS system by the way.
help would be appreciated many thanks volt
Hi all
Sounds spot on but if you can test on the supply side of the RCD without using 'no trip' (assuming it's within the DB) then your PFC reading will be more accurate.
The black lead on the 1553 will stay connected to the neutral bar throughout the 2 tests.
Your PEFC and PSSC should be almost identical on a TN-C-S system.
Im a bit confussed now :) ahh forgive me i just noticed on the megger the top hole has the NO TRIP LOOP so this would be the neutral which would be connected thoughout the test ? correct ?
So the test would be a 3 lead test in reality then ? not a 2 as i thought ? is this correct ? many thanks volt
I wasn't too clear there, if you can perform the test without using 'no trip' then it's a 2-lead test.
Using 'no trip' it's a 3-lead test.
I tend to use the Hi setting on the megger (- 4th along on the green area of the dial, if you know what I mean.) 2 lead test for PFC to earth and neutral
Don't need to link leads on the megger just have red & green plugged in.
Sent from my iPhone using Tapatalk.
yeah i can what you mean on the megger says HI PFC LOOP so this way i could just use RED and GREEN leads ?
So the test would be LIVE TO EARTH ?
LIVE TO NEUTRAL ?
LIVE TO NEUTRAL ?
that's how it is on the 1552. don't use no trip.
Reading through the megger leaflet quick start guide reguarding this PFC TEST
non tripping loop test [NO TRIP]
Select when testing ciruits with RCD protection fitted it says
High current loop test [HI]
for use on circuits with no RCD protection fitted
No trip PFC measurement [NO TRIP PFC]
phase to earth PFC
yes, but you only use no trip when measuring after the RCD, not before it
Thanks i get it now :)
So the test i would use on my TNCS system and the consumer unit being a MK dual RCD board would be
To set the megger onto the HI loop setting into the green area
then test form LIVE TO EARTH then LIVE TO NEUTRAL and record the highest reading as my PFC ?
spot on. remember this test is done with the main switch OFF, and all earths connected.
Correct (as long as it is before the rcd) you can do either the 2 lead or 3 lead test before an rcd , but it has to be the 3 lead , no trip option after an rcd.
Yeah thanks for that much aprreciated guys got their in the end :) but its so important to make sure its right you have no other option than to be ---- about it [ as one of a better phrases ] :D
I mean obviously im new to this but once i get my inspection out the way i want to take the level 2 testing and inspection to boost my confidence then maybe onto the level 3.
Thanks once again guys for all the replies much appreciated and very helpfull.
Perfect attitude, pity the perpetrators of much of the certification that I come across didn't have the same pride!
Reply to P.F.C using a megger 1553 advice plz in the Industrial Electricians' Talk area at ElectriciansForums.net
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Hi All, Ive just got my results through and I failed my first attempt of AM2 exam on the live testing of inspection and testing. I passed...