Hi everyone.
Please can someone explain how i calculate the output ac voltage of an appliance?
If a power supply adapter shows output volts as dc how do i work out the equivalant output volts in ac?
Thanks
 
If the appliance has a DC power adapter then there's a very high chance it won't work with AC and you'll probably cause damage to it if you try. There are a few exceptions to this rule but the appliance would be labeled with an AC and DC supply option accordingly if that were the case. If you're still in doubt rather contact the agent of the appliance.
 
Not sure what you would gain from this? Or why you would want to, in with regard to pat testing. I've done abit and nearly slit my wrists in the process.
 
Hi, thanks for your reply. I understand that appliances <50v ac dont need pat testing but how do i work out the output ac voltage if it only shows on the output as dc v on the adapter. Thanks
 
Not sure if I've fully understood you here, but: Are you asking about the output of DC adaptors (power supplies)? If so, then are you trying to decide whether the items of equipment powered by the adaptor in question should be PAT tested??? Daz
 
Hi Daz.

Yeh i am trying to figure out what actually needs testing. mayb i'm getting a bit confused.
eg. power adapter for phone.
AC Adapter
INPUT: 230VAC ~ 50Hz 8W
OUTPUT: 5VDC ⎓ 300mA 1.5VA

thanks
 
Hi,

You are confused. The plugtop is 230V , that's the bit you need to check; you aren't going to PAT test the phone are you!

If you had a 230Vac -25Vac Transformer, would you test it?

Regards.
 
R.M.S. = D.C./√2 (No load)


How the hell is anyone supposed to write an equasion with bloody auto bloody correct?
 
Hi,

You are confused. The plugtop is 230V , that's the bit you need to check; you aren't going to PAT test the phone are you!

If you had a 230Vac -25Vac Transformer, would you test it?

Regards.

No, caus its under 50V ac?
(its an office phone)