Steve22

Hi am doing my first periodic inspection for a restaurant, my understanding is that I need to test a percentage of installation, so can I test some circuits and leave others? And if I could perform a certain test on a circuit how can I fill the schedule of results? Thanks
 
Depending on the age and condition of the installation, it could be 100% of circuits need to be tested.

Paperwork from previous tests is a good place to start if they are available
 
The percentage test is 100% unless the client has decided otherwise.
 
Depending on the age and condition of the installation, it could be 100% of circuits need to be tested.

Paperwork from previous tests is a good place to start if they are available
The installation to be honest looks in a good condition, the problem is I could find any paper work from previous tests, and some circuits I can't power them off to do all tests, and now am confused how to fill the schedule of test results
 
Anything you cant inspect or test write it in limitations. On the schedule of results insert LIM into the sections you can’t do
 
percentage testing means testing a percentage of points on each circuit, but all circuits need to be tested. it does not allow for any circuits to not be tested at all.
 
I thought all circuits initially need fully testing no excuses

Then once you have done this you can agree to test a certain percentage of circuits at regular intervals
 
You can "not test" a circuit, for instance it is quite normal not to turn off a comms supply. However, use your initiative. In a restaurant its probable that there is little you cannot test, on the certificates there is a box which says operational limitations
 
Out of hours I never have problems turning off comms cabinets.
Depends on what companies you are working for, You could still do a Zs reading, I've worked for many a company that don't want you to turn their equipment off, depends on the company
 
We did an EICR a few years ago, everyone was happy we were turning power off and on etc, Monday morning, 2 network switches had blown their power supplies, just due to power off, power on,
 
Too many limits though and you end up with a piece of toilet paper.
You should have a really good reason for not powering down a circuit, just limiting circuits means you could be leaving potentially dangerous circuits in play.
 