Hi Guys,
Appreciate the comments, I am the engineer that carried out the EICR on this property. My doubts were raised over the the BS 4293 having overload protection, if the device did not have overload protection I would have no alternative but to give a code 1. BS 4293 were replaced with the BS EN 61008 standard and listed as an RCCB. Rather than just failing the board on these grounds I felt I should research it first. After researching it on the internet I found much conflicting detail due to the age of the devices. I have attempted to locate federal electric technical help but to no joy. I contacted the NICEIC technical helpline however they could not give details of specific units and I was to refer to the manufacture.This article by the IET states that a RCCB has no integral overload protection http://electrical.------.org/wiring-matters/15/insp-test-rcd.cfm . If anyone has any literature or information relating to this it would be much appreciated. I also understand the comments of the costing I quoted for changing the consumer unit, that is my choice given the extent of works already carried out and the simplicity of the install, given I already have the dead test values typed up on Amtech it is only a couple of hrs local work and screw fix offer dual RCD consumer units for £58.99.
Many Thanks
Hi Guys,
Appreciate the comments, I am the engineer that carried out the EICR on this property. My doubts were raised over the the BS 4293 having overload protection, if the breakers did not have overload protection I would have no alternative but to give a code 1. BS 4293 were replaced with the BS EN 61008 standard and listed as an RCCB. Rather than just failing the board on these grounds I felt I should research it first. After researching it on the internet I found much conflicting detail due to the age of the devices. I have attempted to locate federal electric technical help but to no joy. I contacted the NICEIC technical helpline however they could not give details of specific units and I was to refer to the manufacture.This article by the IET states that a RCCB has no integral overload protection http://electrical.------.org/wiring-matters/15/insp-test-rcd.cfm . If anyone has any literature or information relating to this it would be much appreciated. I also understand the comments of the costing I quoted for changing the consumer unit, that is my choice given the extent of works already carried out and the simplicity of the install, given I already have the dead test values typed up on Amtech it is only a couple of hrs local work and screw fix offer dual RCD consumer units for £58.99.
Many Thanks
rite...i think i`v seen enough of this crud...
go back to college will you.....
You'll have to excuse the terminology, I did try to edit prior to anyone seeing that, clearly not fast enough. I really would appreciate some serious advice.
do these devices have an amperage rating on them, e.g. 15A, 30A etc.? if so, they're RCBOs and have O/L and S/C protection.
Thanks telectrix
I also thought that but a standard RCD also has an ampere rating Ie : In: 63 A, Ideltan: 30mA so I couldn't accept it on face value, the only thing i could go off was the BS number which leads me to believe it is an RCCB.
difficult to tell from the photo, but i can't imagine it was installed with no OCPDs for the circuits in question.
Reply to Periodic inspection in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone, I recently moved out of my rented property, and as expected, my landlord is attempting to withhold a significant portion of my...
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
I don't fit alarms as my main job but have fitted quite a few over the years whilst we were doing the electrics side of things. I usually fit the...