Hi
One of our room lights got reported flashing intermittently and then would not work. I have checked at PIR and only 150v there is 240v at switch at com and L1 when switched. Even though its only 1 way switch. 2 cables coming in grey- com, L1 -brown, L2- black
At PIR grey - neut, Black and brown - live in and out
Replaced PIR and switch and the lights still not working
Thanks
 
Tried linking out pir which made no difference
Used multimeter between neutral and live in on pir and between earth and switch terminals
 
If linking out the PIR made no difference it probably didn't need replacing. You need to do some continuity tests.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
wales

Thread Information

Title
PIR AND SWITCH Fault
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
8

Thread Tags

Tags Tags
switch

Advert

Thread statistics

Created
bjl,
Last reply from
westward10,
Replies
8
Views
103

Advert

Back
Top