The problem only occurs at night,when tested during the day everything works fine.

No heat sources (still waiting for the plu...erm water guy..to connect up the boiler) and sensor's well away from any flue's when boiler is finaly connected. It's at an empty bungalow thats being done up with the client going there at night painting etc hence the calls telling me they wont reset.

they're stand alone sensors from wholesalers (Friedland L220NBLK 200deg (just found delivery ticket in me pocket))....definitely leaning towards the latching problem, blowing my brains abit the fact it's only a problem at night and not in the day.
 
The problem only occurs at night,when tested during the day everything works fine.

No heat sources (still waiting for the plu...erm water guy..to connect up the boiler) and sensor's well away from any flue's when boiler is finaly connected. It's at an empty bungalow thats being done up with the client going there at night painting etc hence the calls telling me they wont reset.

they're stand alone sensors from wholesalers (Friedland L220NBLK 200deg (just found delivery ticket in me pocket))....definitely leaning towards the latching problem, blowing my brains abit the fact it's only a problem at night and not in the day.

that maybe the problem,cheap pirs,they wont trip thru day due to photocell but at night they will pick up anything,heat from next doors flue moving trees/bushes etc
 
How long has this been occurring?

Reason i ask is some PIR's have a over-ride function where they will operate as a normal floodlight for 6 -8 hours. You usually activate this function by switcing them off - on - off - on within a couple of seconds............just a thought
 
The problem only occurs at night,when tested during the day everything works fine.

No heat sources (still waiting for the plu...erm water guy..to connect up the boiler) and sensor's well away from any flue's when boiler is finaly connected. It's at an empty bungalow thats being done up with the client going there at night painting etc hence the calls telling me they wont reset.

they're stand alone sensors from wholesalers (Friedland L220NBLK 200deg (just found delivery ticket in me pocket))....definitely leaning towards the latching problem, blowing my brains abit the fact it's only a problem at night and not in the day.

That's why I asked if you had tried covering BOTH photocells together and not one at a time, as this would simulate darkness.
 
Admittedly i haven't covered both cells at the same time...i'll try that tommorrow in daylight (or more like dull daylight the way the weather is) and see what happens.

Could be the cheap £15 PIR's....out of interest any suggestions on quality brands of stand alone PIR's?
 
Admittedly i haven't covered both cells at the same time...i'll try that tommorrow in daylight (or more like dull daylight the way the weather is) and see what happens.

Could be the cheap £15 PIR's....out of interest any suggestions on quality brands of stand alone PIR's?

id cover them both at night,that will point to either a faulty unit,or if its picking up,decent kit is gjd,more expensive but false alarm free

External Detectors | CCTV Detection | IR Illuminator
 
I had a similar'ish problem a while back. On reading the installation instructions back it mentioned something about masking part of the sensor blah de blah and guess what (taped the part of the sensor that was pointing towards the other light) That worked, I don't know the exact reason why but I presume it may have been something to do with the one light setting the other off?

Not sure if this is related to your issue though?

How far apart are the two lights/sensors?

How far away from fascias etc?

;thumbsup
 
Problem finaly solved, was a mixture of possible faults that i finaly sorted out with a trip there tonight whilst dark (luckily job is only 10 mins up the road)

Tried numerous things as suggested in this thread earlier today with no luck (inbetween doing other jobs on site to save going nuts), so decided i had to return this evening when it's dark to see whats going on. Basicaly it's down to a mixture of 2 main problems i've decided:-

A) cheap sensors that only have lux (night-day) setting and time setting but no sensitivity setting.
B) Next door neighbours light (odd i know).

The neighbour has a corner light he leaves on all night to shine over his car....to aid the picture of the cheap CCTV camera he has looking over it. The light shineing off his car was effecting one of the PIR's (found it hard to believe meself tbh), so i installed one of the shields on the PIR (as suggested by 1shortcircuit) and problem solved....lights time out as required and alls good.

Many Thanks to all who stopped me going totaly nuts (halfway there already) and thank god thats sorted!

:grouphug:
 
Problem finaly solved, was a mixture of possible faults that i finaly sorted out with a trip there tonight whilst dark (luckily job is only 10 mins up the road)

Tried numerous things as suggested in this thread earlier today with no luck (inbetween doing other jobs on site to save going nuts), so decided i had to return this evening when it's dark to see whats going on. Basicaly it's down to a mixture of 2 main problems i've decided:-

A) cheap sensors that only have lux (night-day) setting and time setting but no sensitivity setting.
B) Next door neighbours light (odd i know).

The neighbour has a corner light he leaves on all night to shine over his car....to aid the picture of the cheap CCTV camera he has looking over it. The light shineing off his car was effecting one of the PIR's (found it hard to believe meself tbh), so i installed one of the shields on the PIR (as suggested by 1shortcircuit) and problem solved....lights time out as required and alls good.

Many Thanks to all who stopped me going totaly nuts (halfway there already) and thank god thats sorted!

:grouphug:

I know exactly how you feel mate, glad you got it sorted and thanks for posting back to let us know how you got on. Always nice to know that our input has helped.

Good job:thumbsup
 
A) cheap sensors that only have lux (night-day) setting and time setting but no sensitivity setting.
B) Next door neighbours light (odd i know).

Glad you got it sorted.
Just a comment about "cheap sensors", I think the ones I frequently use are actually the same item:
Spectra - 200 deg PIR Sensor 1kW Load - Black

They're one of the few PIRs that I've found that haven't given me any troube. Certainly better than the ones on cheap PIR floods that have a sensitivity setting. So I wouldn't discount them on the basis of this slightly unusual problem.
 
That Spectra PIR looks exactly the same as the friedland ones i've fitted...likely same factory different box scenerio.