Hi guys,

Quick question, I've had some people say to earth a plastic junction box with piranhas etc. whereas some people saying there's no need, since it's plastic?

I have the 5 terminal adaptable junction box from Screwfix (image attached)

From the inside of the house I have twin & earth coming into the box, connecting to 2 runs H07RN pond flex which is then going to be run to the outdoor lights in plastic conduit and with glands.

If it's confusing I can make a diagram?

Thanks
 

Attachments

  • C203CE9E-B12B-448F-AAA7-70349E3C27FA.jpeg
    C203CE9E-B12B-448F-AAA7-70349E3C27FA.jpeg
    250.1 KB · Views: 130
You don't earth the plastic box, and you don't use Piranha nuts, since you aren't using armoured cable. However, the CPC (ie. Earth) needs maintaining throughout the wiring system.
 
I like that AB with the factory screws never seen them. Bloody marvellous ?
 
Don't earth the box, but make sure there is continuity on the CPC by linking the incoming and outgoing CPC's together.
 
Made by Speslberg. Many types are available with fitted terminals but usually single-row as they are targeted at mainland Europe where single-row are more widely used.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Plastic Junction Box earthing?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
JiSingh12,
Last reply from
Lucien Nunes,
Replies
4
Views
2,915

Advert