Sub question, why did lots of older installs (not in bathroom) use selv for lighting. E.g kitchen or lounge lights selv. Was this 15 or 16th edition req? Sorry i am a bit of a youngster!!

Ed

12 volt light were available before GU10 and the brass ones were all the rage in the 90s
 
Sub question, why did lots of older installs (not in bathroom) use selv for lighting. E.g kitchen or lounge lights selv. Was this 15 or 16th edition req? Sorry i am a bit of a youngster!!

I believe it's as follows:
At one time, if you wanted a halogen lamp, the only ones available were ELV, which is why they're still widely installed.

Reliable 12V and 24V halogen lamps are much easier to make than 230/240V, as the filament is thicker to carry the higher currents required. They have been used on automotive applications since about 1970 (maybe earlier?) and I'm guessing that they were then introduced to building lighting because of their improved efficiency, colour rendering, and smaller physical size compared to ordinary tungsten filament lamps. Only later did the technology develop to manufacture sufficiently reliable LV halogen lamps.
 
We went to do a kitchen rewire in old council flat. Rewireable board, instead of putting in new board to provide RCD protection for my work i decided to run 6mm 'clipped direct' from unused 45a fuse in existing board to submain just below the existing board. This submain has RCD and 32a mcb for our 4mm radial for the kitchen. So discrimination is ok (i think?!?!)

By the way- I did IR test on existing board and N-E wasnt satisfactory which is why i didnt put new whole board in.

Seems a nifty way to fulfil regs in old installs seeing as you only take responsibility for the circuit you work on
and you wouldnt get the job if customer asked for a few extra sockets and you said they needed a rewire! Yes, i would recommend it as a highly recommended option obviously.

Bloke who works for firm i work for says if you do an upgrade like for e.g new circuit you must put in a whole new board. I am sure i'm right and he's not. But humble enough to admit if i'm not!! What u all think?!

Thanks girls & boys,

Eddie

So what you're actually saying here, is sod the the unsatisfactory IR tests, i've found a way to get around the problem of upgrading the safety of the installation as a whole, i'll just ignore what i've found!!

So Yeah, really nifty of you!!

I'm just wondering if this other electrician is being taken out of context in what he's said, especially if he knew that you had done a cover-up job, instead of upgrading the main CU as was originally planned??
 
Not really a cover-up job. I informed customer of latent defects and suggested a workaround. Better than a cowboy just whacking new circuit in old board with no rcd protection and better for customer than a rewire which they def couldnt afford and wouldnt do. Engineer54 i was trying to find a good compromise whilst still complying to regs at all times. We all know the REAL world of sparking is v different to the IET offices' perception!!!!!
 
Not really a cover-up job. I informed customer of latent defects and suggested a workaround. Better than a cowboy just whacking new circuit in old board with no rcd protection and better for customer than a rewire which they def couldnt afford and wouldnt do. Engineer54 i was trying to find a good compromise whilst still complying to regs at all times. We all know the REAL world of sparking is v different to the IET offices' perception!!!!!

to be honest i'd do the same, well i'd give the customer the option, X hours fautfinding & new board at £XX then i'll fit the sockets, or fit a new board and work from that for £XX amount. some would go for the expensive "proper" way, mos would just want the cheap job!
 
The trouble is, he's still been the last to work on an installation which he has found, after his own testing, was in a potentially dangerous condition.
 
Ok maybe that was a bit flippant but i reckon if isolated N-E fault then V unlikely to be dangerous as they are at v similar potential. If i'm completely wrong come at me! I am keen to learn, thats why i'm here.
 