Discuss polarity testing in the UK Electrical Forum area at ElectriciansForums.net
is it
a. the test ensures all fuses, signle pole switches and themo are connected in L only. although this doesnt apply to the swa. but it checks all three lines are correcftly identifiied throught the system
b. for safety reasons.
Pretty much......but add to b. that you wouldnt want to energise an installation with incorrect polarity.....and regarding a. you are checking the polarity of the SWA according to the question,not the entire system.
Correct sequence for safe domestic electrical testing
BEFORE CONNECTION OF THE SUPPLY
Continuity of protective conductors
Main and supplementary bonding continuity
Continuity of ring final circuit conductors
Insulation resistance
Site applied insulation
Protection by separation
Protection by barriers and enclosures
Insulation of non-conducting floors and walls
Polarity
Earth electrode resistance if an earth electrode resistance tester is used
WITH THE SUPPLY CONNECTED
Earth electrode resistance if an earth-fault loop tester or the ammeter and voltmeter method are used
Confirm correct polarity
Earth-fault loop impedance/PFC/PSSC*
Correct operation of residual current devices
15
Correct operation of switches and isolators
to put it simply, if you test it dead and the readings are good, there's less chance of it going bang when you switch on.
Visually check all connections so you know all connections are in the correct terminals, and all connection are Identified.3 core swa correctly identifed (Brown Black Grey - Brown Blue Green/Yellow).
Umm, what about prospective fault current, seems to be missing from the above list (to be verified before switching any circuits on)?
My instruments display both so I guess it's classed as one...anyone?
But added, will be emailing the company to add it to their web site !! No Hope..
Step 13 both PEFC/PSSC, to ensure that all your protective devices are suitably rated before energising.
Edit: PFC->PEFC.
Polarity
15
Have never liked the phrase "with the supply connected", alot of people get this confused with turning on the main switch, whereas steps 11,12 and 13 should all be carried out with installation isolated
You mean circuit isolated surely, ergo mcb in CU, but then try doing a polarity check/eli/pfc/pssc with the power not energised?
Reading too deep into this its the methods to get the correct polarity, on 1 garage supply...not a full installation...
My understanding of the term PFC (prospective fault current) is that it is the higher of the PEFC and PSCC, so you normally just list "PFC" which is taken to mean you measure both PEFC and PSCC and record the highest. Alternatively you could list out "PEFC" and "PSCC" and still just record the highest. (For a single phase system, at least).
No, he does mean installation isolated, at this point. The supply should be connected to the CU, but the main CU switch should be in the off position.
Before adding a circuit you should carry out a test on earth fault loop impedance (Ze), for which you should be disconnecting the earthing conductor so installation needs to be isolated
Reply to polarity testing in the UK Electrical Forum area at ElectriciansForums.net
Hi, I've recently done a PAT course after the large company I work at discovered we have a Deltapat 3309 kit tucked away. I'm actually an...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...