I need to run a dedicated line for a pool pump which would be about 140 ft from the outside panel. Pump requires 14-15 amps at 2HP. Should I run a 20 or 30 amp breaker and with what gauge wire? Plan to DIY with some help and would like to use conduit. Any advice is much appreciated!
 
volt drop would be your main concern. get it wrong and the motor will stall and burn out. we use metric size cable. without more detail, e.g. what voltage and is it single phase? but i'd make a educated guess that you will need 8 gauge or 6 gauge. a US member (megawatt for one) will advise you better.
 
1
volt drop would be your main concern. get it wrong and the motor will stall and burn out. we use metric size cable. without more detail, e.g. what voltage and is it single phase? but i'd make a educated guess that you will need 8 gauge or 6 gauge. a US member (megawatt for one) will advise you better.

120V and I believe single phase? It's a plug in pump it that helps.
 
120V will be single phase. over here we use metric cable. 10mm is similar in size to your gauge 8. 16mm is about 6 gauge. top of my head you'll need 16mm ( 6 g.) to limit your volt drop to around 6 V, i.e 5% of 120V. this is our max. prmissible % drop for non-lighting circuits. as before, a US electrician may advise you better.
 
120V will be single phase. over here we use metric cable. 10mm is similar in size to your gauge 8. 16mm is about 6 gauge. top of my head you'll need 16mm ( 6 g.) to limit your volt drop to around 6 V, i.e 5% of 120V. this is our max. prmissible % drop for non-lighting circuits. as before, a US electrician may advise you better.
Timluts you need a 30 breaker and # 10/2 with a ground underground approved for direct burial wire and is it 240vac or 120 vac motor ?
 

Reply to Proper wiring for a pool pump in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

After 24 years my septic lift station pump and high water alarm needs to be replaced. It was tripping the breaker and the alarm was no longer...
Replies
5
Views
654
I have a 20 amp gfci pool pump breaker that trips only when the pump is off during the night. Pool pump runs fine all day. I turn pump off...
Replies
2
Views
746
Hi All, We've done some electrical in the past. Wired our outdoor kitchen, added an electric heater to our porch, etc. We are pretty new to pool...
Replies
3
Views
1K
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
763
Hello! My shop is currently on a single 15 amp circuit. Is like to upgrade it at the main home panel to a 30 amp. Do I just need to run 10 gauge...
Replies
1
Views
647

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock