The logic of pulling the E.7 tails would apply to the normal supply, if you don't trust the main switch working.
Minimum required;
Prove continuity on the E7 Main switch whilst ON.
Switch off and prove NO continuity.
If you're replacing C.U or tails, work as you would for a normal supply.
Cool, that's what I need - how would you do that, please? Isolation test across the switch, both L and N?
test continuity on both poles. with switch open then closed.
Loss of continuity would prove the switch is working.
Not been rude.....
That should have been a fairly obvious one
Yebbut I don't like to think thoughts like "well it's obvious" around safe isolation.
And with due respect I don't think it is that obvious because mere loss of continuity at closure doesn't prove the airgap will withstand the supply voltage. Hence my suggestion of actually IR testing rather than continuity testing. I know this may appear pedantic but I'd rather be a live pedant than an electrocuted whatever-a-smoking-corpse-that-when-alive-was-not-a-pedant-is-called.
Where it all gets really confusing is when you have an economy 10 supply... It kicks in for a few hours a couple of times during the day...
An IR Test would be just as quick,
do both, would still be quicker than writing your OP.
Also if you turn all the breakers off you will have double protection whilst working and no load if it was to energise, so it wouldn't hurt to much anyway
- pulling the cutout fuse (would you do it if you were being assessed though?)
tut tut tut
1) do you carry approved seals to reseal the cut out?
2) under your risk management what do you do with the live side which you could insert a BS finger?
3) have you not read the 17th edition OSG which states that the cutout fuse is not to be removed by electricians and only by a supplier?
Now if you are really worried about the failure of the main switch carry out your usual procedure for proving its dead, you know live source, dead source, live source. Then when you are happy IR test both poles with the isolator open and closed at 500volt or 1000 volt if you really want to.
Incidentally why do you want to do this? what are you doing to the board?
If you still have problems ask a grown up to help and do remember side cutters can be sharp!:daisy:
Ring the DNO and wait for them to fit a isolator.
which can then be turned off
don't megger that because it will be live, unless you pull the fuse to check it
I was testing an E7 system a few months ago and then at 3pm, just as I was finishing, the timer switched it on. Thankfully I didn't have my fingers in the board at the time. lol
I had exactly the same thing, all packed up and noticed the neons were on on the spurs for the storage heaters, spoke to the owner and she said its a kind of boost in the afternoon, nice if her to let me know.ad I was changing the off peak board
But how will he know that isolator is operating correctly?
Modern Insulation Resistance Testers will not work on a live circuit. Whats all this talk of pulling the fuse, nobody illegally does that.. do they? lol :)
Thats why im packed up and gone by 2.30! :wink5:
That's the best way to do a fast board change when you know it'll go live any minute.