chloebear

Hi all,

Got a bit of a strange one - just been to a house that has had a new CU fitted and they are having problems with one of the ring circuits - if you plug in a standard lamp it pulses fast, not enough juice to run the TV if you plug it in either????????
anyone got any good ideas???????
 
Check your voltage / Zs the circuit could be a neutral fault make sure nothings plugged into the circuit , also do a Ze test as this could be a fault on the neutral of the supply TNCS ,When loading the voltage is dropping ,
 
Last edited by a moderator:
Agree check voltage on circuit and Zs.
 
Last edited:
all other circuits in the house seem to be Ok, I will be returning in the morning to continue the investigation, just looking for pointers & if anyone has come accross this before. Could a mixed leg & leg on the line conductor cause this??
 
Does sound like you have low voltage on that circuit. Keep us posted with your findings.
 
turns out that the cause of the problem with pulsing standard lamps on the ring cct was due to the line conductor being connected to a breaker on the main switch side of the board and the neutrals being connected to the RCD side of the board. MK board with dual RCD protection, the RCD had tripped into its mid way state and was causing this effect. Solution for the time being was to re-connect the neutrals to the non rcd protected side of the board and hey presto no problems. I also discovered why the ring cct was places on its own breaker on the non RCD side - there is quite a large leakage cpc/Line on this cct, so I guess it was causing a lot of nucance tripping. Next stage is to find out the cause of this problem.
 
turns out that the cause of the problem with pulsing standard lamps on the ring cct was due to the line conductor being connected to a breaker on the main switch side of the board and the neutrals being connected to the RCD side of the board. MK board with dual RCD protection, the RCD had tripped into its mid way state and was causing this effect. Solution for the time being was to re-connect the neutrals to the non rcd protected side of the board and hey presto no problems. I also discovered why the ring cct was places on its own breaker on the non RCD side - there is quite a large leakage cpc/Line on this cct, so I guess it was causing a lot of nucance tripping. Next stage is to find out the cause of this problem.

But if the RCD was tripping in it's 'mid-way' state, shouldn't you be a bit concerned as to why it's not completely tripping out?
 
MK ones dont go all the way down when they trip, they stop at half way. To reset you need to push the switch all the way down and then back up.
 
MK rcds have 3 states of operation (or not) fully up is in normal operation mode, tripped halfway is standard trip mode & to reset the trip you have to toggle the switch into the down position and then reset to the fully up position.
Dont know why - just a standrd of the MK rcds.
 

Reply to pulsing lamps in the Australia area at ElectriciansForums.net

Similar Threads

Morning All Got little bit situation going on, causing multiple visits (luckily only 2 mins drive from where we are.) Client not 100% happy with...
Replies
9
Views
975
Hello! I design and build lamps, which has been a simple task so far, but I've decided to dip my toe into the dubious world of 120v LED PCBs for...
Replies
0
Views
760
Hello I have some decking lights which to be fair, have been nothing but pain in the bottom since they were installed. Moisture in the lens lamps...
Replies
10
Views
2K
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
795
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
601

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock