So, a final stab at getting my point across.
Take a 10 kw item of current using equipment, now that could be anything because in my world it doesn't matter.
At 240 volts it draws (10,000/240)= 41.67 amps
Now lets look at it at 210 volts (10,000/210)= 47.61 amps
You cannot arbitrarily decide that this 10kw thing is now anything other than a 10kw thing. It is what it is. Either the power over time is going to be exactly the same or the output/performance of it is going to be affected.
I can't for the life of me see any way past that. Maybe I'm thick or I've forgotten a lot of the theory I learnt as a boy but for me the maths and science can't be changed.