RonanIrl: I found this installation video:
RHI-(3-5)K-48ES - https://solisinverters.com.au/product/rhi-3-5k-48es/
Could you look at it and tell me any similarities or differences? At the moment I am particularly interested in the bits at 5min08s on the data stick (-do you have one?) and from 5min15s onwards on the meter and current clamp.
This is also interesting on how the Solis hybrid inverter reduces its power output at the temperature rises:
Inverter Temperature De-rating - https://usservice.ginlong.com/support/solutions/articles/36000074739-inverter-temperature-de-rating
You will see a table which says that the inverter degrades in power and then shuts down at 60C. Food for thought. But you do not it seems get an OV TEMP fault code or alarm which is perplexing.
I note your inverter, at least beneath it, does not have the minimum 300mm clearance and there is what looks like pyramid loft insulation.
PS: I declare now: if it was my installation, it would not be in the loft.
RHI-(3-5)K-48ES - https://solisinverters.com.au/product/rhi-3-5k-48es/
Could you look at it and tell me any similarities or differences? At the moment I am particularly interested in the bits at 5min08s on the data stick (-do you have one?) and from 5min15s onwards on the meter and current clamp.
This is also interesting on how the Solis hybrid inverter reduces its power output at the temperature rises:
Inverter Temperature De-rating - https://usservice.ginlong.com/support/solutions/articles/36000074739-inverter-temperature-de-rating
You will see a table which says that the inverter degrades in power and then shuts down at 60C. Food for thought. But you do not it seems get an OV TEMP fault code or alarm which is perplexing.
I note your inverter, at least beneath it, does not have the minimum 300mm clearance and there is what looks like pyramid loft insulation.
PS: I declare now: if it was my installation, it would not be in the loft.