RonanIrl: I found this installation video:

RHI-(3-5)K-48ES - https://solisinverters.com.au/product/rhi-3-5k-48es/

Could you look at it and tell me any similarities or differences? At the moment I am particularly interested in the bits at 5min08s on the data stick (-do you have one?) and from 5min15s onwards on the meter and current clamp.

This is also interesting on how the Solis hybrid inverter reduces its power output at the temperature rises:

Inverter Temperature De-rating - https://usservice.ginlong.com/support/solutions/articles/36000074739-inverter-temperature-de-rating

You will see a table which says that the inverter degrades in power and then shuts down at 60C. Food for thought. But you do not it seems get an OV TEMP fault code or alarm which is perplexing.

I note your inverter, at least beneath it, does not have the minimum 300mm clearance and there is what looks like pyramid loft insulation.

PS: I declare now: if it was my installation, it would not be in the loft.
 
Power in from solar and battery is 5.6kW and power out for consumption and export to grid is 5.16kW - a difference of 0.44kW being apparently dissipated as heat in the inverter box

Hello M - just triggered me on the conversion efficiency of the Invertor. For sure no Invertor is 100% efficient and these readings imply 1- 44/560 = 92%. So 8% in heat, hmmm ... smoking gun? :)
PV Inverter cutting off array sunny days 61603118-7D3D-43E4-8E15-E3F06C06B8CB - EletriciansForums.net
 
See below answers


Could you give me some other days when the inverter stopped generating power please -

May 30
June 2/16/19


what I have noticed is that if one looks at inverter internal temperature and dc voltage pv1 against time for the 18 Aug 20, the drop in pv1 voltage co-incides with the inverter internal temperature reaching 59.8C. There is this notice under the 'Temp' tab the bold, underlined italicised text is relevant:

--->
IGBT (Core) Temperature
When IGBT temperature is lower than its max. tolerance temperature, inverter can run stably.

Inverter Ambient Temperature
Inverter internal air temperature

Notice: Usually, IGBT temperature is 20 ℃-30 ℃ higher than inverter ambient temperature.

<---

So, maybe at maximum generation, on a hot day in your loft the IGBT(Core) temperature is of the order 59.8 + 30 = 90C. All semiconductors ( in this case an Insulated Gate Bipolar Junction Transistor IGBT) have maximum junction temperature limits of the order 150C-175C. Normally the semiconductor devices are operated at temperatures much lower than the maximum in order to safeguard their reliability and lifetime. See: First few paras of:

https://www.analog.com/media/en/training-seminars/tutorials/mt-093.pdf

There will necessarily be a thermal gradient between the junction of the IGBT (a semiconductor power switch necessary for the conversion of dc into ac) and the the ambient air flowing of the heat sink of the inverter box. It may be then that at on very sunny days, with high ambient temperature in the loft and peak pv power generation the IGBT core temperature has been exceeded causing a shutdown of generation.

Have a look at the plot for 18 Sep 20 of DC voltage PV1, Ac Output Total Power and internal temperature C against time. You will note a period of very high pv generation (6.3kW) before the shutdown and a steady rise in temperature. The generation starts again when the internal temperature is 40C. The generation does not look stable, fluctuating markedly, which seems odd to me on a clear very sunny day without clouds. Could you post this plot for others to look at who may be following this thread - I cannot do it for some reason.

The IGBT temp is a new measurement in the last firmware and SOLIS have looked into this already for my issue it was same on the old inverter so its not that accoring to them. The invetrer livese in a dark cold plant room so termpertaure there is never above 20, ite well ventillated and no heat sources on warm days.

Anyway, to pursue this line of analysis I need some other times/days when the inverter shutdown to see if the same correlation is apparent. :)
[/QUOTE]
 
See Responses Below

https://voltaconsolar.com/DOWNLOAD-FILES/Solis/Solis-RHI-(3-5K)_Installation Manual Voltacon.pdf

1. Re: Fig 3.3 - Meter Communication socket - Is anything connected to this socket?
Yes black plug heading off somehwre

2. Re: Your # 37 - the power figures do not balance. Power in from solar and battery is 5.6kW and power out for consumption and export to grid is 5.16kW - a difference of 0.44kW being apparently dissipated as heat in the inverter box - if the readings are correct. Rather a lot of thermal heating inside the inverter box.

Dont owrry about that i had the backup meter swithed off in options ithis includes heat energy, internal energy to run the inveter and engery diverted to a second backup battery if instaleld, now I turned it back on the figures balance I actually had my installer on the blower about it last night and asked him why they didnt add up, once i enabled backup measurment again it did weird...id say he is sick of me by now.

3. It appears from the power figures that at least one of the grid power or consumption powers is being measured in order that the other can be recorded. Maybe the consumed power is being measured by a current clamp and not the export grid power. Could you have a look around the consumer unit for a clamp - no need to open it up. It would be helpful if you took some photos and post them for me to look at of your loft inverter installation, your supply metering, inverter metering and consumer unit being careful to capture the cable routes and switchgear. And also for the data logger.

At the moment im not in a position to acces the loft.. i do know there are clamps up there but could be anywhere on the long runs. Also gained this nugget of info on the call with the installer.
 
Responses as below

RonanIrl: I found this installation video:

RHI-(3-5)K-48ES - https://solisinverters.com.au/product/rhi-3-5k-48es/

Could you look at it and tell me any similarities or differences? At the moment I am particularly interested in the bits at 5min08s on the data stick (-do you have one?) and from 5min15s onwards on the meter and current clamp.

Yes i have a data stick thats how the appa and webiste portal receive info via my wifi and firmware updates are deployed by SOLIS or me manually if sent.

Yes the meter is plugged in but clamp is up in the loft somwhere

The system is deifitly setup to know when grid is available and lines are clamped to measure


This is also interesting on how the Solis hybrid inverter reduces its power output at the temperature rises:

Inverter Temperature De-rating - https://usservice.ginlong.com/support/solutions/articles/36000074739-inverter-temperature-de-rating

You will see a table which says that the inverter degrades in power and then shuts down at 60C. Food for thought. But you do not it seems get an OV TEMP fault code or alarm which is perplexing.

Solis looked into this also and said its not the issue that said inverter hyper clipping was my initail though what could be causing this


I note your inverter, at least beneath it, does not have the minimum 300mm clearance and there is what looks like pyramid loft insulation.

Its actualy in a cold plant room dark side of the house, 1m from the ground Pyramids are sound proofing for my boiler which is in the same room but obviously off in summer. Sound pyramids give little insulation as they are open cell. Fault was happening well before the sound insulation was installed.

The air can circulate via vents an its always below 20 in there even in sumemr.

SOLSI and my installer have looke dat temperatrure and both came back as negative causing the issue.




PS: I declare now: if it was my installation, it would not be in the loft.
[/QUOTE]
 
I agree the inveter cooling sink can get hot but accoring to SOLIS and the installer no hotter than any other installtion they have done and not the cause of the problem.



Hello M - just triggered me on the conversion efficiency of the Invertor. For sure no Invertor is 100% efficient and these readings imply 1- 44/560 = 92%. So 8% in heat, hmmm ... smoking gun? :)
View attachment 60838
 
This afternoon I observed your real-time power figures for Generation, Grid, Battery and Consumption. It has clearly been very sunny where you live because the generation figures have been up in the 5-6kW range. The temperature of the inverter has exceeded 60C and you have had a shutdown of generation.

What I observed was 4600W output from the inverter to the CU; 900W consumption from the CU; 3700W export.

4600 = 900 + 3700.

With such high solar generation the battery should not be being discharged yet it was at a rate of 170W - this is not right. There is ample solar to supply the load and any export.

Here is the wrinkle; your installation is not set up to export because the backflow power is set to +0000W. And yet it is exporting - why?

I reckon the current sensor which monitors the glow of grid power into and out of your home is orientated the wrong way around - they have an arrow to indicate the supply and the CU direction - you could check this easily.

It might be though that the current clamp is orientated the correct way but its leads have been wired into the meter (which relays data to the inverter meter comms socket via an RS485 cable) the wrong way.

The wrong orientation of the current sensor or a switch over of its leads will reverse the sense of the data input on grid power flow so the inverter will interpret an export as an import and an import as an export.

For the self consumption mode of operation, any grid import is offset by the injection of inverter ac power of an amount conditional on the kW limit of the inverter pertaining at the time and the incident sunshine on the panels. The inverter does not use power from the battery for export to the grid - this battery is solely for home use.

A negative feedback loop controller ramps up PV generation until the ac output power cannot be increased any further. As the ac output power increases the imported power should reduce and if there is sufficient pv generation to zero import. However if the sense of the signal is incorrect the imported power signal rises and rises because it is actually representing export of the very same increased pv generation - a positive feedback loop - ie: export power becomes maximised. The inverter starts to get hotter.

When one studies the ac output power plot it cycles between maximums and a minimums in a way determined by the temperature related power output derating scheme, incident sunshine changes and load changes in the home. Eventually the inverter shuts down (or becomes unstable at higher temperature and looses sync with the mains) . It cools down, restarts and then carries on again.

Power figures right now: Gen 3.25kW, Load 0.9kW, Export 2.25kW Battery discharge 0.15kW
 
Last edited:
RonanIrl - you have seen this in my email to you.

Yes I did see the shutdown. I was observing the data and 'fortunately' I saw it happen. I hope my explanation in my last post of the EF makes sense; you must have covered positive and negative feedback which will be used in aircraft system controllers.

What made me explore positive feedback through an incorrectly orientated grid power flow sensor was the apparent oscillation of the total ac power output between peaks and lows when there was little home load; it could only mean this high solar power generation was being exported because it was not being consumed nor charging the battery because as noted the battery was discharging - something you noticed.

Once I had confirmed you were exporting shed loads of power in the self use mode in an oscillatory manner the most likely reason was going to be the sensor mistaking import for export and changing negative feedback into positive. The other give-away was the gradual temperature rise - it went over 60C when ac output was some 6kW - which instigates the derating of the power output to prevent damage to the power electronics.

An indicator was the pv1 current mimicked the total power generation (which was being maximised for export) and not the home load - for self consumption, once battery charging is subtracted it should follow the home load only - negative feedback control system in action to minimise imported grid power but never export.

Other key factors - all worked properly overnight when there was no pv generation available for export - as noted the battery will not be drawn on to export. At the moment the 150W odd discharge is making up for the inverter power losses and measurement errors.

What I do need to check further is you seem to be charging your battery from the mains sometimes - need to confirm but I don't suppose you want that to happen - I would not unless you have cheap rate electricity overnight that makes it worthwhile. I saw it during the day too though.
 
All,

So the enginerr just left the house after testing and replacing a few things.

  1. All firmwares updated
  2. 1 shunt remoewd and 2 new wired in as they now belive the shunt was faulty and cutting off the PV array due to overheat, asked them to install one each string thsi time and move them lower in the attic to a cooler area which they did. Model Projoy PEFS-EL55-4
  3. All wiring and connections checked inclduing all of clamps which there are 3, 2 for th eedi and one for the battery system allocated in my CU, They all checked out and were correctly installed. He also confirmed gauge and lengths for me... inverter to CU 6mm at 12M length, Cu to Meter 16mm approx 7 M Length, DC strings to Inverter 4mm at 7 M Length, not posisble to check Meter to Transformer as it is sleeved.
  4. All EPM Backflow and bettery mode setting checked and were all correct.
They are almost 100% sure the shunt was the problem so lets see. Seems they cut off at 70 degrees temp inside the enclosure and frankly my loft where they were installed right at the peak could be 35 ambient on a super sunny day so perhaps that added to the power flow heating caused the shutdown. Although the manual says the shunt if it shuts down for temp must be manually reset by removal and reapplication of the AC voltage which seems to indicate power on and off cycle in the hosue which hasnt happened to date yet it had come on by itself again so who knows!!

If it is not the problem then they will adjust the country setting to increase to outbond voltage to be higher just in case it too low and our inbound is higher when exporting. Although we need to ask the network provider for permisison to do this but they always say yes if told why.

He did mention there is a fault code associated with grid voltage too high and it hasnt thrown that code ever OV-OG or something so he doesnt think that is the issue.
 
Thank you for the update. If it alright with you I will log in every so often and observe the system? - the next very sunny day here (maybe where you are too) is tomorrow Sun 20 Sep 20.
 
Guys just to close this issue the movemmeg of the fireman switch shunts lower in my loft and the installation of one on each string seems to have solved the issue.

Appears they were exceeding their operating temp and shutting off on sunny days due to heat trapped in the loft.

Wont know 100% until nect summer but so far looks good.
 

Reply to PV Inverter cutting off array sunny days in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock