why are you using a makeshift extension lead ? your tester should be enough to test the cables not energizing a known faulty cable !!!!
i`v told you how to dry it already.....when i disconnect the piro from the connector block with singles going to the consumer unit the rcd holds. as soon as i touch the piro line to the single line. rcd trips.
i'm sure its damp too but really wouldn't know how to dry it. and i'm sure it could happen again anyways
yep and once i dry it out. who's to say it wont happen again in a week or two???
my megger only goes up to 450v.
nope trips straight away. its so strange because there are three runs of pyro on the left of the hall doing it, and one run on the right of the hall.
i think i will just replace it anyway because, i'm guessing theres a chance it will get damp and trip again anyways even if i did dry it. now that you have said that i'm always certain that it is a damp issue. but would damp cause a dead short???
yep and once i dry it out. who's to say it wont happen again in a week or two???
like i said i have disconnected all of the socket faces and it still trips, so can't be the socket/spur plates.
tony mc i've got a megger mft1710 and only IR tests at 250v and 500v, so to answer your question no it doesn't test at 1000v.
tony its all very well you saying i should look at my testing method without actually giving me any advise on what you would do?
like i said i've identified where the first leg is, disconnected it and done a 450v IR Test??? as soon as i reconnect the line to the db it trips.