hi,
i want to design non-automatic transfer switch by 2 contactors and push buttons.
my question is do i need mechanical between the 2 contactors? or it is enough to work with NO-NC for both contactors.
please help me
 
hi,
i want to design non-automatic transfer switch by 2 contactors and push buttons.
my question is do i need mechanical between the 2 contactors? or it is enough to work with NO-NC for both contactors.
please help me

Hi mate,

usually an electrical interlock is sufficient. I think an additional interlock is only required by cranes, FLTs etc.
Hope this will help.:)
 
thanks very much
more details:

I need this to work between generator and main , it is not manual with handle and also not ATS.
can i count on wiring the NO for the first contactor with NC for the second contactor and vice versa
so when the first is on the second is off and when the second is on the first is off.
i don't want the main power get into the generator
 
i would personallyhave a mechanical interlock, as i have experienced contactors sticking to NO or NC before, and you would'nt want both supplies to energise together ect!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Question about non-automatic transfer switch
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Sayedahmed,
Last reply from
johnstantine,
Replies
8
Views
2,586

Advert

Back
Top