Hi all can anyone tell me where the values for r1+r2 for swa are in the regs or onsite guide, can't find them, thanks chris
There are no R1 + R2 values for any cables in the regs, as that is determined by a formula that contains length so you either need to measure or calculate it.
Cable manufacturers websites have the info on resistance of the steel armour when used as a CPC on them.
There is also info here......
Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.
Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
15
16
17
2.5
5.7
17
19
20
21
23
35
24
36
40
41
44
49
16
36.1
46
50
72
25
36.1
60
66
76
35
36.1
66
74
84
50
56.4
74
84
122
70
79.0
84
119
138
95
107.2
122
138
160
120
135.3
(131)
150
220
150
169.2
(144)
211
240
185
208.6
(201)
230
265
240
270.6
(225)
(260)
299
300
338.3
(250)
(289)
(333)
400
403.9
(279)
(319)
(467)
Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.
Conductor CSA
1.5
3.4
16
17
18
2.5
5.7
17
19
20
19
21
23
22
23
36
26
39
43
16
36.1
41
44
49
25
36.1
42
62
70
35
36.1
62
70
80
50
56.4
68
78
90
70
79.0
80
90
131
95
107.2
113
128
147
120
135.3
(125)
141
206
150
169.2
(138
201
230
185
208.6
(191)
220
255
240
270.6
(215)
(250)
289
300
338.3
(235)
(269)
(319)
400
451.0
(265)
(304)
(452)
You may find this table useful
R1R2 Values
as an aside
You need the following information
1/ Resistivity of the steel wire
2/ Length and csa of steel wire
3/ Ambient temperature correction factors, usually stated at 20 deg C
4/ Running temperature of the cable usually stated at 30 deg C
5/ Operating temperature of cable , usually 90 Deg C or 70 deg C depending on XLPE or PVC, respectively
R1+r2 values for steel wired armour
Australia
schoe,