Hi all,

Quick question when doing r1+r2 testing wether its a new install or a EICR, is there a table to show maximum readings we should be getting? Or is it a calculation?

Thanks in advance

Luke
 
If it's a new install then maximum values of Zs and VD should have already been calculated.
On a periodic inspection your prime focus is on values for compliance with ADS.
 
Appendix I OSG, Appendix B GN3
Those these are the theoretical values so expect a slight variation in practice, but they do give you a guide to likely values.
On an EICR it is unlikely you could get near to estimating the length of circuit installed.
 