Rampantchilli
My regs book is in my van, so can't check the details, but with R1R2 readings that high I would assume bad connections all round, seeing as it is pretty certain that its builder wired. Someone on here will be able to tell you the expected resistance per meter of 2.5 t&e.
the Zs readings are acceptable as long as you have 30mA protection on the circuits, provided that your earth electrode is within tolerances, and not relying on main bonding to bring the Zs down.
I would suggest to the customer a full EICR with 100% of the accessories checked, and explain everything to them, verbally and in writing.would be good to hear what you find
the Zs readings are acceptable as long as you have 30mA protection on the circuits, provided that your earth electrode is within tolerances, and not relying on main bonding to bring the Zs down.
I would suggest to the customer a full EICR with 100% of the accessories checked, and explain everything to them, verbally and in writing.would be good to hear what you find