My regs book is in my van, so can't check the details, but with R1R2 readings that high I would assume bad connections all round, seeing as it is pretty certain that its builder wired. Someone on here will be able to tell you the expected resistance per meter of 2.5 t&e.
the Zs readings are acceptable as long as you have 30mA protection on the circuits, provided that your earth electrode is within tolerances, and not relying on main bonding to bring the Zs down.
I would suggest to the customer a full EICR with 100% of the accessories checked, and explain everything to them, verbally and in writing.would be good to hear what you find
 
no i checked all six lives for continuity and same for others neut and earth

- - - Updated - - -

cant get to wires above as barn conversion no loft
 
Forget the length theory. This is clouding your judgement mate. Go and do some socket investigation. If they are genuine radials then split them onto separate 20a and make sure you dont exceed the floor area limits. Also assess what sort of loads these radials will serve. You may need to run some legs and convert into rings if the demand is questionable or if you do not have the C.U space to accommodate so many radials.
 
Could there be a section where the rings have not been connected and plastered over? Do they still have a copy of any drawings if its 7 months old
 
Sounds like you need to go back to basics and check everything. Fingers crossed the owner has deep pockets.

Yeah, but my experience is that those with deep pockets also have short arms, that's why their pockets have gotten so deep :ihih:
 