when i try to test an RBCO at the DB it trips as soon as the test probes touch the terminals, this only seems to happen with Bill/MEM RCBOs, it doesnt happen with Merlin or Square D. I'm using a standard Robin RCD tester. Any idea why???
 
seem to remember a thread a while ago that some RCBOs needed the fly lead disconnecting . not too sure exactly what it was . i don't use many RCBOs, myself.
 
its so annoying, its ok if i test at a socket but when your working alone testing in long corridors going back and forward on 1x and 5x, 0 degrees and 180 degrees....its a bit of a pig!
 
so's the ex-wife. glad i don't have to reset that any more.
 
Try disconnecting the outgoing cable from the RCBO and put a short length of wire in the terminals and test from there. Had the opposite problem on a MEM RCBO where I couldn't get it to trip at all so may be a similar issue. Worth a go anyway.
 
It could well be due to the electronics in the meter if you are putting one probe on at a time it may cause an imbalance when the second probe is connected ,try switching off the RCBO putting both your leads on then switching back on and then testing just a thought
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
shotton, flintshire

Thread Information

Title
RCBO Question...
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Dean Williams,
Last reply from
nickblake,
Replies
5
Views
1,539

Advert

Back
Top