Had a strange one the other day.

I was in a main switch room and had an RCBO connected into a DB, but switched off. From it was a radial in singles to a socket adjacent to the DB. The conductors were disconnected at the socket, if I touched the neutral down to earth, it sparked as though it was live, and the Main LV panel behind me started to hum.

Why was this happening?
 
A photo might help. If there was a flash between the neutral and earth then either the neutral is floating at a voltage wrt earth or the earth isn't actually at 0 volts. The RCBO doesn't appear to be providing isolation possibly either.

Sounds like it might be a good time to drag out the testers before it nails some other poor soul.
 
Ok I forgot to mention, when I tested it I had 0v between L and E, but 2v between N and E.

The RCBO was in the off position when this was happening.

BTW, all live tests passed.
 
TN-S

I'd have thought that with the RCBO switched off, there would not be any possibility of any potential difference between L N or E. Evidently not in this case.
 