Shurbunkin
When you did the IR tests did you leave all the cpc's connected to the cu?
No I didnt. I turned all MCBs off. Will try that
When you did the IR tests did you leave all the cpc's connected to the cu?
No I dontHave you got an earth leakage clamp metre?

IR fault on an adjacent RCD controlled circuit?
No I didnt. I turned all MCBs off. Will try that
I think this may be the case as well. Will need to head over there again and spend a couple of hours testing the rest of the circuits one last time
Check any hard wired appliances like boilers, extractor hoods etc are disconnected as well. Not just switched off.
That's a good idea. Ill isolate the fans, cooker hood and boiler from the circuits and see what happens. That maybe the reason. I find when I fault-find I always look at the worst case and take them apart instead of just looking at the simple possibilities. It wastes a lot of timeI think this may be the case as well. Will need to head over there again and spend a couple of hours testing the rest of the circuits one last time