S
Shurbunkin
Hello
I am new to the forum and was hoping I could pick your collective brains.
I am an electrician with 7 years experiance. I have mainly worked for the MOD and on commercial and industrial builds throughout my time.
I now do the odd bit of domestic work and need some help on a kitchen ring main I have installed.
The circuit is wired in 2.5mm twin and earth. The circuit is protected by a 32b MCB and a 63amp RCCB covers this and a bank of 5 other circuits.
I have tested the ciruit with a fluke tester and the readings have all come back perfect. Low continuity values. Insulation resistance tests clear. Fault loop impedance test came back at 0.54 ohms. (Max 1.16 ohms)
When I turn the circuit on the MCB and RCCB holds fine but as soon as I plug something in the RCCB trips. I thought this was strange as the circuit tested out fine and all the other circuits on the RCCB work fine aswell. I disconnected all the neutrals from the other circuits and left all circuits off but the kitchen circuit, but still when load is applied the RCCB trips.
I don't have a lot of experience with testing but know enough to get by, I thought. I have asked fellow electricians and they suggested the RCCB or MCB was faulty so I have changed them both. Still the probem persists.
Any ideas what the issue may be?
Thank you for your help in advance
Fellow sparky
If you have not got your neutrals mixed up then I would say a neutral to earth fault based on it trips out when plugging something in.
Some further easy things to check:
1. Test RFC IR L-E and N-E.
2. The IR of load you are using to test the RFC.
3. Polarity L-N at each socket. Modern sockets switch the N first and L second on closing and L first and N second on opening.
4. Undo but do not completely remove the securing screws on each socket. Then carefully pull back on the socket and look inside to check whether the RFC live conductors, N especially, are touching the securing screws. Then remove the screws completely and examine the state of the insulation of the live conductors for damage due to screws, or nipping or sharp edges.
5. Tightness and solidity of all RFC connections. Make sure the insulation of the live conductors ends before entering the terminal holes.
6. Check tightness and solidity of 32A MCB and RCD in/out connections including to busbar.
7. Where cable sheath has been cut back to check the condition of insulation on L and N. Any small nicks?
Isn't late break, early make the other way round? The source of energy (the L) is disconnected first then the 'escape route' for the energy (the N) is disconnected a fraction of a second later?
That's how @marconi described it. Neutral is closed first and opened last.
Thank you all for you suggestions
are there any appliances plugged into the circuit? you mention it is under load?
I only had my 110v transformer plugged in so thought maybe there was a fault with it but took it apart and looks fine. Plugged into another socket circuit and worked fine. So I then plugged the site hover into the troublesome cicuit and it tripped so it a circuit issue, not an appliance
I will thoroughly test the other circuits again and see what I can find. Strange thing is they are all on and under load. The kitchen ring main is the only one that has problems, and that tested out fine as well.
The next thing will be to take all socket fronts off to see if theres a socket screw in a cable as suggested. Although would insulation resistance test find this?
I will take a picture of the CU when im next on site and post it. Need to make sure it looks pretty :)
Thanks again