Hello
I am new to the forum and was hoping I could pick your collective brains.
I am an electrician with 7 years experiance. I have mainly worked for the MOD and on commercial and industrial builds throughout my time.
I now do the odd bit of domestic work and need some help on a kitchen ring main I have installed.
The circuit is wired in 2.5mm twin and earth. The circuit is protected by a 32b MCB and a 63amp RCCB covers this and a bank of 5 other circuits.
I have tested the ciruit with a fluke tester and the readings have all come back perfect. Low continuity values. Insulation resistance tests clear. Fault loop impedance test came back at 0.54 ohms. (Max 1.16 ohms)
When I turn the circuit on the MCB and RCCB holds fine but as soon as I plug something in the RCCB trips. I thought this was strange as the circuit tested out fine and all the other circuits on the RCCB work fine aswell. I disconnected all the neutrals from the other circuits and left all circuits off but the kitchen circuit, but still when load is applied the RCCB trips.
I don't have a lot of experience with testing but know enough to get by, I thought. I have asked fellow electricians and they suggested the RCCB or MCB was faulty so I have changed them both. Still the probem persists.
Any ideas what the issue may be?
Thank you for your help in advance
Fellow sparky
If you have not got your neutrals mixed up then I would say a neutral to earth fault based on it trips out when plugging something in.
Some further easy things to check:
1. Test RFC IR L-E and N-E.
2. The IR of load you are using to test the RFC.
3. Polarity L-N at each socket. Modern sockets switch the N first and L second on closing and L first and N second on opening.
4. Undo but do not completely remove the securing screws on each socket. Then carefully pull back on the socket and look inside to check whether the RFC live conductors, N especially, are touching the securing screws. Then remove the screws completely and examine the state of the insulation of the live conductors for damage due to screws, or nipping or sharp edges.
5. Tightness and solidity of all RFC connections. Make sure the insulation of the live conductors ends before entering the terminal holes.
6. Check tightness and solidity of 32A MCB and RCD in/out connections including to busbar.
7. Where cable sheath has been cut back to check the condition of insulation on L and N. Any small nicks?
Isn't late break, early make the other way round? The source of energy (the L) is disconnected first then the 'escape route' for the energy (the N) is disconnected a fraction of a second later?
That's how @marconi described it. Neutral is closed first and opened last.
Thank you all for you suggestions
are there any appliances plugged into the circuit? you mention it is under load?
I only had my 110v transformer plugged in so thought maybe there was a fault with it but took it apart and looks fine. Plugged into another socket circuit and worked fine. So I then plugged the site hover into the troublesome cicuit and it tripped so it a circuit issue, not an appliance
I will thoroughly test the other circuits again and see what I can find. Strange thing is they are all on and under load. The kitchen ring main is the only one that has problems, and that tested out fine as well.
The next thing will be to take all socket fronts off to see if theres a socket screw in a cable as suggested. Although would insulation resistance test find this?
I will take a picture of the CU when im next on site and post it. Need to make sure it looks pretty :)
Thanks again
I think this may be the case as well. Will need to head over there again and spend a couple of hours testing the rest of the circuits one last time
This is when having an earth leakage clamp meter helps - I think they are essential these days.
Check any hard wired appliances like boilers, extractor hoods etc are disconnected as well. Not just switched off.
o_O That's a good idea. Ill isolate the fans, cooker hood and boiler from the circuits and see what happens. That maybe the reason. I find when I fault-find I always look at the worst case and take them apart instead of just looking at the simple possibilities. It wastes a lot of time
I was fault finding a circuit last week because a switch had stopped working - on the switch drop there was no continuity on any of the 3 cores , IR at one end was OK, but at the other end the IR had a dead short N-E.
A new set of shelves had been put up......
A drill had gone through the cable completely!
The end of the cable with the dead short wasn't connected to anything so wouldn't have shown up on any tests .....
Given its a kitchen circuit, has Kev the fitter damaged a cable for you?
I'm assuming that the IR tests you've carried out have all been fairly short tests... press the button, get the result kind of affair?
Can you continue the test, maintaining the 500v for a while?
I've had a couple of cases where the test appears to be satisfactory, but if you apply the test voltage for a longer time the charge builds up to a point where it jumps a pinhole in the insulation and the IR momentarily drops. Not so easy to see on digital test gear if there isn't a virtual analogue display, but visible on my Megger's virtual analogue meter in the LCD.
To help us mull over this problem could you tell us the type of supply and earthing system, the presence and state of EP bonding and provide a picture of the intake and CU innards please?
As Murdoch said, it would be really helpful if you could borrow an earth leakage clamp meter to do some measurements, for example standing leakage for each final circuit, and then total leakage less kitchen FRC, and then finally total leakage for all FCs.
Also could you post some figures for your measurements of IR?
Is all the wiring and are all the wiring accessories on the kitchen ring new? Have there been any water leaks?
Kings Lynn
RCCB tripping when under load problems
Shurbunkin,
marconi,